I think I know the answer already, but I'm looking for reassurement. I'm installing two 20A circuits in a back yard. Due to length of runs, I will need to increase conductors of one of the circuits to #8. According to 250.122(B), I need to divide cmil of #8 by cmil of #12 and multiply the answer by the cmil of the minimum required EGC for a 20A circuit shown in Table 250.122. Great, I get to use #8 for my EGC for a darn 20A circuit.
I have two arguments of why this is crazy.
I have two arguments of why this is crazy.
- The #12 EGC requirement for a 20A circuit is already super conservative, and I'm guessing this stems from 240.4(D). I'm wondering why there isn't an exception to 250.122(B) for 15, 20, and 30 amp circuits.
- I'll be running these circuits in EMT, and I don't even need to run an EGC according to 250.118(4). However, I like to run EGC's no matter what the conduit type, so because of that, I'm now required to bump the EGC to #8.