Here's the scenario...
2" riser containing 19 current carrying conductors(includes neutral count), 1 EGC, and a 4 spare condutors.
This is for a lighting load, the longest run is probably 200'.
All circuits are single pole 20A @ 277V.
CBs have a 75 degree rating.
What would you say the MINIMUM wire size (THHN) would be?