  1. Replies
    19$$
    Views
    854

    Oh that's already been done. A contractor friend...

    Oh that's already been done. A contractor friend bought some "arc faults" at Depot. When he opened them up they were regular breakers with a curly # 14 white inserted under the load screw.
  2. Thread: Fire pump

    by GerryB
    Replies
    2$$
    Views
    326

    Thanks, I'll try it:)

    Thanks, I'll try it:)
  3. Thread: Fire pump

    by GerryB
    Replies
    2$$
    Views
    326

    Fire pump

    Does any one know what year the code required fire pump ocp to indefinitely carry the locked rotor current? I have a 93 NEC. It doesn't have Art 695 but it does state in 230.90 (a) exception 4....
  4. Replies
    16$$
    Views
    1,061

    Why? Don't think I've ever heard of 3 phase as...

    Why? Don't think I've ever heard of 3 phase as being enjoyable:lol:
  5. Replies
    5$$
    Views
    356

    You actually don't need a breaker in the attic....

    You actually don't need a breaker in the attic. Put in a $15 pull out disconnect.
  6. Replies
    5$$
    Views
    356

    As a contractor I would never get involved with...

    As a contractor I would never get involved with stuff like that past the breaker, ie appliances, hot tubs (especially hot tubs:)), but maybe it's yours or a friends. Maybe you could bypass the attic...
  7. Replies
    38$$
    Views
    2,599

    But you're scheduled for Friday?

    But you're scheduled for Friday?
  8. Replies
    33$$
    Views
    1,272

    It does also say condensation and leaks, and as...

    It does also say condensation and leaks, and as Dennis said it doesn't address a flush mount installation. Maybe OP should ask the inspector, if it's an insurance job he probably needs a permit.
  9. Replies
    33$$
    Views
    1,272

    I interpret the dedicated space as "working...

    I interpret the dedicated space as "working space", to safely work on the equipment, not about keeping water from a leak going on it. You could have plumbing on the floor above, a toilet or washing...
  10. Replies
    7$$
    Views
    2,223

    So is there a listed connector? Or could you just...

    So is there a listed connector? Or could you just secure the cables within 8" of the box and use a chase bushing?
  11. Replies
    3$$
    Views
    570

    Those old cables I've seen were always copper, so...

    Those old cables I've seen were always copper, so 55a or 65a.
  12. 0-10 VOLT DIMMING

    I have a similar question. Can you bring a CLP-3 conductor into a 277 volt switch to feed. The switch has power leads and the dimming leads on it, so how do you separate .25 inch. The MC luminaire...
  13. Thread: AC vs. MC cable

    by GerryB
    Replies
    5$$
    Views
    483

    Definitely the aluminum is much lighter. Back in...

    Definitely the aluminum is much lighter. Back in the day you were expected to carry 2 rolls of bx, one on each shoulder, up to whatever floor needed it. MC lite, no problem.:)
  14. A lot of electricians are surprised to find out...

    A lot of electricians are surprised to find out (myself included one time) that mc cable is basically the same as romex when it comes to physical protection. Is it a lot below 6'? I don't know where...
  15. Replies
    3$$
    Views
    325

    310.15(B)(3)(a), 310.15(B)(16), Table C9,...

    310.15(B)(3)(a), 310.15(B)(16), Table C9, 310.15(B)(3)
  16. Replies
    3$$
    Views
    325

    I would say you could do that. 3" looks good for...

    I would say you could do that. 3" looks good for nine 3/0 conductors. You need to derate for more than 3 current carrying conductors. 3/0 copper at 75 degree chart is 200amps, so 400 amps derated at...
  17. Replies
    18$$
    Views
    966

    Which was stated in post #3. If it is not boxed...

    Which was stated in post #3. If it is not boxed or safed off it is the inspectors business if you are looking for a final.
  18. Replies
    18$$
    Views
    966

    Rough in is fine. OP is looking for a final with...

    Rough in is fine. OP is looking for a final with a wire laying on the floor.
  19. Replies
    18$$
    Views
    966

    The OP didn't say he had no disco under the sink...

    The OP didn't say he had no disco under the sink or on the counter.
    Are you in Vermont? A friend I know recently built a house there. He had to have the service (underground) inspected but not the...
  20. Replies
    18$$
    Views
    966

    That's how it would be here, same with a hood and...

    That's how it would be here, same with a hood and blanks over not installed fixtures.
  21. Thread: Six handle rule

    by GerryB
    Replies
    17$$
    Views
    1,169

    2017 nec c Connecticut finialy adopted.this March...

    2017 nec c Connecticut finialy adopted.this March 1 2019 Actually Ct. adopted it Oct 1, 2018. Pretty sure they adopted the 2014 in Oct of 2016. They may be trying to catch up in 2020.
  22. Replies
    25$$
    Views
    2,110

    I think 2014 also, 680.42(C) as you noted says in...

    I think 2014 also, 680.42(C) as you noted says in part "equipment grounding conductor that is insulated or enclosed within the outer sheath".
  23. Replies
    25$$
    Views
    2,110

    I think he is talking about Art 680, maybe...

    I think he is talking about Art 680, maybe 680.21(A)(1) You need an insulated ground for a pool motor(or Spa)
  24. Replies
    25$$
    Views
    2,110

    Wouldn't that rule out using UF cable?

    Wouldn't that rule out using UF cable?
  25. Replies
    8$$
    Views
    571

    Standard BRK or Kidde, I don't plan on doing...

    Standard BRK or Kidde, I don't plan on doing this, it's just something I recall being said. The job is an open ceiling and easily corrected the right way.