  1. Replies
    34$$
    Views
    1,956

    I have brought this up many times and no one...

    I have brought this up many times and no one around here counts that clamp in P&S boxes. The way the code is written I think that they should be counted. IMO, it depends on whether the box volume...
  2. Replies
    34$$
    Views
    1,956

    One has to assume the mention of a clamp means to...

    One has to assume the mention of a clamp means to count it but as I said earlier this is not a good question. At least the OP understands what he needs to look for. You can't always guess what a...
  3. Replies
    34$$
    Views
    1,956

    Yep-- look at 314.15 in the nec

    Yep-- look at 314.15 in the nec
  4. Replies
    34$$
    Views
    1,956

    10- 14/2 cables = 20 conductors x 2 = 40 ...

    10- 14/2 cables = 20 conductors x 2 = 40

    grounds and clamps count as 2---- 2x2 = 4

    Total 44
  5. Replies
    34$$
    Views
    1,956

    You count the grounds one time and the cable...

    You count the grounds one time and the cable clamps one time. Bad question because are you to presume there are devices in the box?