    So, Mr Hildenbrand, does section 2 actually say...

    So, Mr Hildenbrand, does section 2 actually say that if you are using a non metallic box, even if you are using cable clamps inside the box, they are not counted, but they have to be designed for use...
  2. Replies
    34$$
    Views
    2,109

    Ok..two not one. Thanks. So six conductors in a...

    Ok..two not one. Thanks. So six conductors in a three gang for yokes, one conductor for all grounds and one conductor for all clamps, then figure out how much is left to figure number of conductors
  3. Replies
    34$$
    Views
    2,109

    Ok, since I am learning and this is one of the...

    Ok, since I am learning and this is one of the things I am learning, let’s see how bad I screw up..12 wire is 2.25... three gang box 44 cubic inches..lol...
    grounds...2.25
    clamps.....2.25
    three...