  1. Replies
    16$$
    Views
    332

    POCO rule maybe, I am not aware of any required...

    POCO rule maybe, I am not aware of any required length of conductor here from NEC.

    "drip loop" is to keep water from following conductor right into the raceway. Simply having the point of...
  2. Replies
    19$$
    Views
    916

    either way you are not using whatever it is as a...

    either way you are not using whatever it is as a raceway, you can run a cable wiring method in about anything and it doesn't need to be listed. If it is exposed you can always say it is providing...
  3. Replies
    13$$
    Views
    581

    If dryer needs a neutral connected then yes it...

    If dryer needs a neutral connected then yes it does carry current. OP's question AFAIK is whether it needs counted as a CCC when it comes to ampacity adjustment purposes. On a 120/240 singe phase...
  4. Thread: towel warmer

    by kwired
    Replies
    7$$
    Views
    276

    yes.;)

    yes.;)
  5. Replies
    18$$
    Views
    925

    As mentioned the heat is supposed to be pumped...

    As mentioned the heat is supposed to be pumped into the water.



    That is something to consider. During cooling season, you are lessening the cooling load on the general environmental space,...
  6. Replies
    14$$
    Views
    490

    Correct. All depends on if it has all the...

    No, a microwave on the counter does not count as permanently installed. So I'm going to say it's probably OK except for the AFCIs.

    -Hal[/QUOTE]Correct. All depends on if it has all the elements...
  7. Replies
    13$$
    Views
    581

    I agree, same appliance generally can be used on...

    I agree, same appliance generally can be used on either system and neutral will be a CCC if supplied from a wye system.
  8. Thread: towel warmer

    by kwired
    Replies
    7$$
    Views
    276

    Well it isn't necessarily the sole determining...

    Well it isn't necessarily the sole determining factor, but certainly can easily change it from damp to wet location if it is easy to get direct spray in the location in question.

    Most the time if...
  9. Replies
    19$$
    Views
    916

    If it is only being used as a sleeve for physical...

    If it is only being used as a sleeve for physical protection it doesn't need any kind of rating, just needs to have suitable strength for the application, which is a judgement call and may not get...
  10. Thread: towel warmer

    by kwired
    Replies
    7$$
    Views
    276

    Unless there is good possibility of direct shower...

    Unless there is good possibility of direct shower spray at the location, why not?
  11. Replies
    41$$
    Views
    2,122

    Correct. Instead of marking it as spare or...

    Correct.


    Instead of marking it as spare or future use why not just "unused"?
  12. Replies
    29$$
    Views
    1,550

    Cheap fixtures from big box stores are not that...

    Cheap fixtures from big box stores are not that heavy.

    Many quality fixtures aren't really that heavy these days either - they aren't the quality they were years ago though.
  13. Replies
    8$$
    Views
    387

    +2 I wouldn't have much issue with metallic...

    +2

    I wouldn't have much issue with metallic Wiremold in many situations like OP described.

    At same time I don't think it is NEC compliant. Damp location can be tricky in many aspects, how much...
  14. Replies
    41$$
    Views
    2,122

    Most such breakers probably don't have ...

    Most such breakers probably don't have designated line and load terminals so it could be used to supply a load, and since it is likely not a plug on breaker you kind of are not backfeeding it.
  15. If you eliminate the primary neutral, are you...

    If you eliminate the primary neutral, are you running two ungrounded primary conductors? For example 12.47kV primary instead of 7.2 kV? If so you really want to have that setup with no low impedance...
  16. Replies
    29$$
    Views
    1,550

    That is my thought, but then more recently they...

    That is my thought, but then more recently they messed with that concept when it comes to paddle fan rated boxes being required in some situations even if a paddle fan isn't going to be installed....
  17. Replies
    7$$
    Views
    426

    My guess it was made for a specific application...

    My guess it was made for a specific application and isn't a general use kind of thing.
  18. Replies
    6$$
    Views
    376

    240.21(B)(1)(1): Seems to me with the...

    240.21(B)(1)(1):



    Seems to me with the "(s)" that was a change in 2014, they intend to allow more than one overcurrent device, but pay attention to required conductor ampacity

    408.36 has...
  19. Replies
    8$$
    Views
    387

    I think it is a grey enough topic that you get...

    I think it is a grey enough topic that you get away with it some places and other places you don't.

    Probably get a higher number of inspectors that say no than yes though.

    Some may say no as a...
  20. Replies
    12$$
    Views
    724

    So are you having actual power loss on one phase...

    So are you having actual power loss on one phase or just losing recording information for some reason on that one phase? Sounds like the latter is what you likely are having, but just trying to...
  21. Replies
    4$$
    Views
    262

    High inertia loads also will act sort of like a...

    High inertia loads also will act sort of like a generator if there is a loss in the normal supply. May not supply the lost leg all that efficiently, but may increase current drawn from working lines...
  22. Replies
    14$$
    Views
    1,021

    It means he refuses to admit he may have been...

    It means he refuses to admit he may have been wrong about something, so finds a way to twist things back to it is your fault if something bad happens, which is kind of true whether he was involved or...
  23. Replies
    27$$
    Views
    1,547

    It is there, but may not have any extreme effects...

    It is there, but may not have any extreme effects in anything you have seen. I haven't really seen any extreme effects either that I can recall.
  24. Thread: Max Breaker

    by kwired
    Replies
    17$$
    Views
    900

    I have a 3 ton heat pump in my house, 45A MOCP. I...

    I have a 3 ton heat pump in my house, 45A MOCP. I have taken readings when in heating mode and it is only pulling around 6 amps.

    I don't know what peak starting current is, but I can tell you it...
  25. Replies
    41$$
    Views
    2,122

    10 feet or 10% of circuit length, whichever is...

    10 feet or 10% of circuit length, whichever is less, you can use the higher ampacity.

    In a situation like OP is in you would need to determine length of each cable, unless a rather large house...