  1. No it is clear in the nec that afci's are not...

    No it is clear in the nec that afci's are not required. Where in the bolded area does it state afci is required for service change. You are not modifying the circuit

    Look at the exception-- NOT...
  2. Replies
    12$$
    Views
    188

    On some units there is a threaded entry for 1/2"...

    On some units there is a threaded entry for 1/2" or 3/4" pipe so the wiring is inside the head of the light. Now that I think about it I believe that is correct
  3. Replies
    12$$
    Views
    188

    If I am not mistaken no box is required for that...

    If I am not mistaken no box is required for that type light. If so just put a pancake box-- there is so much space there that using a box is inane, IMO. There are usually 4 mounting holes at the...
  4. Replies
    7$$
    Views
    318

    Here for one Also

    Here for one




    Also
  5. Replies
    7$$
    Views
    248

    Here is a good look t the different wires. Of...

    Here is a good look t the different wires. Of course nm-b comes in yellow, white, orange , black




    ...
  6. Replies
    7$$
    Views
    248

    Is the jacket gray in color or some other color...

    Is the jacket gray in color or some other color like black, white etc...


    https://www.cerrowire.com/wp-content/uploads/2018/06/cerrowire_product_sm_c_nmb.png ...
  7. Replies
    7$$
    Views
    248

    Where did you get 2/0 nmb. I thought they only...

    Where did you get 2/0 nmb. I thought they only made it up to #2
  8. Replies
    12$$
    Views
    383

    I get it you want a momentary relay not really a...

    I get it you want a momentary relay not really a momentary switch. All the switches are momentary as they just push the relay in and out with air. You want one that stays on as long as you have...
  9. Replies
    12$$
    Views
    383

    Amazon has it for under $30.00 ...

    Amazon has it for under $30.00
    ...
  10. Replies
    12$$
    Views
    383

    Plumbers always supply those switches and they...

    Plumbers always supply those switches and they buy them at the plumbing supply place. I can't imagine an air switch that is not momentary

    This is what we see
    ...
  11. Replies
    6$$
    Views
    175

    Welcome to the forum. I don't know what UL508A...

    Welcome to the forum. I don't know what UL508A is but the nec does not allow a #4 on a 100 amp breaker as a feeder.

    Load x 1.25 if the loads are continuous =96A thus you need a conductor good for...
  12. No, the nec does not require the panel to be...

    No, the nec does not require the panel to be replaced unless there is some reason it won't work- perhaps an old fuse panel, etc. AFCI are not required to be replaced unless there is work down on the...
  13. Replies
    2$$
    Views
    141

    Feeders or branch circuits. Also look at 110.21...

    Feeders or branch circuits. Also look at 110.21 and 110.22
  14. Replies
    8$$
    Views
    223

    You could do that but again the connections will...

    You could do that but again the connections will be difficult. Why not push for plastic. The metal seems absolutely insane.
  15. Replies
    7$$
    Views
    318

    No, the service can be 6000 amps and the ground...

    No, the service can be 6000 amps and the ground rod only needs to be 5/8" x 8' or 1/2" by 8' if listed. BTW, welcome to the forum
  16. Exactly, the section states overhead conductors...

    Exactly, the section states overhead conductors not raceways. 35 years, or so, ago I had an inspector red tag my job because the meter base was mounted next to a window. I called him up and he...
  17. Replies
    8$$
    Views
    223

    Wow, that would be a pain. IMO, you should...

    Wow, that would be a pain. IMO, you should insist that the grates be plastic
  18. If this is a service calculation then I would use...

    If this is a service calculation then I would use 200 watts


    [/INDENT]


    Depends.. if you are calculating for conductor size then I would use the Table value at 120V. You can try and...
  19. Thread: Sleeves

    by Dennis Alwon
    Replies
    48$$
    Views
    1,173

    Steve, IMO that install is fine however, as...

    Steve, IMO that install is fine however, as others have said there will be an inspector somewhere that will turn it down. We use regular pvc not schedule 80---
  20. Thread: Hot tub

    by Dennis Alwon
    Replies
    1$$
    Views
    195

    I am closing this thread, in accordance with the...

    I am closing this thread, in accordance with the Forum Rules.If you feel this action to be in error, feel free to contact me via PM to explain.eminder to all members, if you see a questionable post,...
  21. Replies
    5$$
    Views
    250

    You cannot run 2 feeders into the panel but if it...

    You cannot run 2 feeders into the panel but if it is a 60 amp 120v feeder you can just jump the lugs or the main breaker so that both sides are hot.
  22. You and Peter have made claims on every afci...

    You and Peter have made claims on every afci thread but neither of you, afaik have done anything to try and change things.
  23. The haters and doubters will never see the afci...

    The haters and doubters will never see the afci as being useful. The fact is they are here and if you hate them then write a proposal to change it but back it up.
  24. There is so much hatred in the industry for afci...

    There is so much hatred in the industry for afci that you will never get everyone to agree on this. Yes, they are expensive but the fact is that in the last 10 years fires and deaths have declined...
  25. Replies
    3$$
    Views
    287

    I agree the inspector is off base on this. Once...

    I agree the inspector is off base on this. Once you are below the buss bars then it is not an issue.