  1. Replies
    9$$
    Views
    187

    You run your conduit before the grid goes up but...

    You run your conduit before the grid goes up but after the black iron and pencil rod is installed. Typically the iron doesn't go up until after all of the duct work is up.
  2. Replies
    9$$
    Views
    187

    In Mrlucky's locale the pencil rod is there to...

    In Mrlucky's locale the pencil rod is there to support the hung ceiling and is installed by a lather. It's also used to support conduit, junction boxes, etc.
  3. Replies
    7$$
    Views
    319

    If you want to go one step further you could say...

    If you want to go one step further you could say that rods are never required. ;)
  4. Replies
    9$$
    Views
    187

    Yes there are no support wires involved here. ...

    Yes there are no support wires involved here. K-12 clips on the pencil rod would be faster than drilling in anchors.
  5. Replies
    9$$
    Views
    187

    One real difference is how it's supported. K-12...

    One real difference is how it's supported. K-12 clips versus fastening to a wall. Also above the ceiling may require working at a heights that requires tall ladders or even lifts.
  6. You could interpolate the difference from the...

    You could interpolate the difference from the tables in Article 430.
  7. Replies
    9$$
    Views
    247

    I took a look at those, look nice but my head is...

    I took a look at those, look nice but my head is spinning. :D

    What color would one normally use for coffered ceiling lights, I'm thinking 2700 or 3000K.
  8. Replies
    6$$
    Views
    175

    No this is not NEC compliant. First you...

    No this is not NEC compliant. First you calculate the load, then the conductor size and finally the OCPD. The OCPD cannot be larger than the conductor ampacity.

    Are you sure that this is a...
  9. Thread: Pool bonding

    by infinity
    Replies
    8$$
    Views
    223

    How close to the pool is this drain?

    How close to the pool is this drain?
  10. Replies
    9$$
    Views
    247

    I'll take a look at all of the links. What is...

    I'll take a look at all of the links. What is typically used to hold the strip in place? I cannot see adhesive tape lasting very long.
  11. Replies
    7$$
    Views
    248

    That's correct #2 is the largest size permitted...

    That's correct #2 is the largest size permitted by the NEC. Must be SE cable.
  12. Replies
    6$$
    Views
    175

    I agree with Dennis but if your using a 75 degree...

    I agree with Dennis but if your using a 75 degree C conductor with 75 degree C terminals you can use #3. You could use the #4 with a 90 amp OCPD.
  13. Replies
    9$$
    Views
    247

    Coffered Ceiling Lighting

    Anyone ever install lighting to light the top edges of a coffered ceiling? Wondering what type of lighting one would use. Some type of LEDs is what I'm leaning towards. End result something like...
  14. Replies
    5$$
    Views
    193

    It's a Con Ed specification cable, 10 conductors...

    It's a Con Ed specification cable, 10 conductors (10 point) all #9 AWG stranded conductors. Yup that is correct, each conductor is labeled #9 AWG with a special 10-point meter color code.

    23164
  15. Replies
    5$$
    Views
    193

    I agree but that was the only place in the closet...

    I agree but that was the only place in the closet that the meter pan would fit. The photo is deceiving there is about 6" of space between the LB and the cabinet next to it which was enough room to...
  16. Replies
    5$$
    Views
    193

    We always do. We just do not connect the Ct's...

    We always do. We just do not connect the Ct's leaving the meter wire for the POCO but we wire the meter pan.

    Here's a 2000 amp service we just did with a 10 point meter pan. 23160
  17. Replies
    7$$
    Views
    319

    How many rods are you installing?

    How many rods are you installing?
  18. Thread: Derating

    by infinity
    Replies
    3$$
    Views
    141

    Yes, I did make some assumptions with the 90...

    Yes, I did make some assumptions with the 90 degree C conductor. A 75 degree C conductor might also work if you can apply the next size up rule.
  19. Thread: Derating

    by infinity
    Replies
    3$$
    Views
    141

    Yes derating is required because you have more...

    Yes derating is required because you have more than 3 CCC in a single raceway. Good news is that you can still use #12 AWG conductors.

    #12 THHN = 30 amps @90 degrees C
    30 amps*70% = 21 amps...
  20. Replies
    16$$
    Views
    553

    That is what was implied but I see that maybe it...

    That is what was implied but I see that maybe it didn't come across that way. I apologize for any confusion.
  21. Replies
    10$$
    Views
    755

    For solid conductors there was nothing better. ...

    For solid conductors there was nothing better. They locked onto the splice and took up less room in the box/fixture, etc. because of their narrow design.
  22. Replies
    16$$
    Views
    553

    That's not his problem. The end user in this...

    That's not his problem. The end user in this case is already using suicide cords. Notice in my first post I said "tell him" meaning tell the customer. KAJ's installation ends at the inlet and he's...
  23. Replies
    16$$
    Views
    553

    How is a short piece of cord with two FEMALE ends...

    How is a short piece of cord with two FEMALE ends a hazard?
  24. Replies
    16$$
    Views
    553

    It's a violation to install it his way so I would...

    It's a violation to install it his way so I would not do it.
    Tell him to make up a female to female adapter to use his existing cords.
  25. Thread: Sleeves

    by infinity
    Replies
    48$$
    Views
    1,173

    Here's what's permitted for protection of NM...

    Here's what's permitted for protection of NM cable:



    Smurf would need to fall under "other approved means" to meet the NEC.