Search:

Type: Posts; User: tom baker

Page 1 of 8 1 2 3 4

Search: Search took 0.08 seconds.

  1. Replies
    16$$
    Views
    555

    I used inlets under the IEC 309 standard, each is...

    I used inlets under the IEC 309 standard, each is unique to the voltage and phase, they are interchange able between manufacturers
    Like this...
  2. Replies
    4$$
    Views
    115

    A well designed and laid out service gear is a...

    A well designed and laid out service gear is a thing of beauty... level across the top of the gear, strut, same type of fittings, conduit...
  3. There is no maximum height, just 6-7 to the...

    There is no maximum height, just 6-7 to the center of the switch from platform,and accessible, and that can be on a second story. Keep in mind the service entrance conductors are unfused and there...
  4. Replies
    9$$
    Views
    607

    208 is 120 to ground. Please see 300.3(C)(1)...

    208 is 120 to ground.
    Please see 300.3(C)(1)
    And the IN at the end, most miss this, and try to use a class 2 circuit with 600 volt insulation in a raceway with power and lighting.
  5. Now you have a second path for fault current,...

    Now you have a second path for fault current, electrically it better to keep the fault current with the circuit conductors to reduce the impedance. We can have a EGC on the outside of conduit for a...
  6. Replies
    25$$
    Views
    1,187

    Electrical loads are decreasing esp with LED...

    Electrical loads are decreasing esp with LED lighting. Non dwelling units typically have services 30% larger than needed as the lighting loads are 3 w sq ft and energy codes are perhaps .5 w sq ft.
    ...
  7. the 83% rule can only be used for dwelling units,...

    the 83% rule can only be used for dwelling units, due to diversity of loads (not all on at the same time)
    The garage feeder has to be sized at 100% as the table saw, sawdust vac and grinder could...
  8. Replies
    20$$
    Views
    2,044

    There is some concern on POE equipment and...

    There is some concern on POE equipment and generating heat in conduits.
    Here is good place to start https://www.bicsi.org
    This magazine had good articles on the subject...
  9. And do you need to ground or bond?

    And do you need to ground or bond?
  10. Replies
    11$$
    Views
    900

    Get the mike holt practice exams. do 100 to 200...

    Get the mike holt practice exams. do 100 to 200 questions per week.
  11. Replies
    18$$
    Views
    1,023

    That issue came up many times starting in 2002,...

    That issue came up many times starting in 2002, and I recall the discussion at the IAEI meeting in Orlando.
    The BC to the smoke needs to be protected the same as any other. I have not seen a post on...
  12. Replies
    15$$
    Views
    801

    Do they work, yes. Ignore everything about...

    Do they work, yes. Ignore everything about nanoseconds and look at jewels to compare

    Mike Holt once said
    You get what you pay for
    More is better

    Mike has some good graphics and I will later...
  13. Replies
    4$$
    Views
    336

    Homeline 120 V 30 amp GFCI

    Not familiar with SQ D Homeline brand, need 120V (single pole) 30 A GFCI for a 30 Amp RV power outlet. My supplier says they are not available, what are my options?
  14. Replies
    19$$
    Views
    983

    Art 520 and Info

    I have used the disposable foam cans, messy, duct seal and fire rated duct seal.
    At work I got a Hilti spray foam gun, expensive but in the long run, not a all. you are able to finely control the...
  15. Replies
    4$$
    Views
    328

    Fluke T5-600, T6-600

    I was about to purchase a Fluke 323 Clamp ampmeter, about $110.

    I don't need to measure over 200A, 600V

    Fluke has a T-5 600 that a fork current clamp, does volts, ohms, for $109
    And the T-6...
  16. Replies
    13$$
    Views
    1,496

    And for a dwelling unit light switch bedroom, the...

    And for a dwelling unit light switch bedroom, the switch does not have to be in the same room, nor a luminaire installed at the lighting outlet.
  17. Replies
    6$$
    Views
    1,035

    Retro Fit T-8 to LED

    Some advice on retrofitting T-8 to LED
    1. Some systems have the ballast removed, and LED lamps wired direct to the tombstones. Are there any listing issues with this?
    2. Use LED lamps that work...
  18. Thread: Home Video

    by tom baker
    Replies
    5$$
    Views
    940

    The monitoring cost is the same as ring, cameras...

    The monitoring cost is the same as ring, cameras a little less. But I like the wireless and cloud storage instead of a DVR...
  19. Thread: Home Video

    by tom baker
    Replies
    5$$
    Views
    940

    Home Video

    I may of asked before, but now being retired I have time to install a video system. I have a Honeywell Ademco VISTA 20 ethernet panel with the touch screen.
    I installed a Ring Video door bell, it...
  20. i agree 100%. I was a member of the IES and...

    i agree 100%. I was a member of the IES and attended the Street and Area Lighting conferences for many years and saw the beginnings of LED in 2008. An HPS or MH lamp is a point source and putting in...
  21. Replies
    23$$
    Views
    1,327

    OK I went to Lowes today. Fan R Us.

    OK I went to Lowes today. Fan R Us.
  22. Replies
    10$$
    Views
    729

    What we find in WA, and our compliance...

    What we find in WA, and our compliance inspectors, is a business (Walmart I know of) contacts with a nation wide electrical contractor for microwaves in breakrooms, they roll thru and install, when...
  23. Interesting, I will wait for Milwaukee as I am...

    Interesting, I will wait for Milwaukee as I am all in on M12 or M18 system
  24. Replies
    9$$
    Views
    1,058

    2200 feet thats a lot of dairy.

    2200 feet thats a lot of dairy.
  25. Our electricians used Light Efficient Designs,...

    Our electricians used Light Efficient Designs, there were a lot of failures, but they started many years ago the products are "better" now.
Results 1 to 25 of 200
Page 1 of 8 1 2 3 4