  1. While it is not done, I agree that the word...

    While it is not done, I agree that the word "maintained" requires some physical method be used to maintain the space between the conductors or cables. Just the fact that there is space is not enough...
  2. The language in the IRC is much like that in the...

    The language in the IRC is much like that in the NEC. It can be complied with without the use of 3 way switches.
  3. While 3-ways are typically installed to comply...

    While 3-ways are typically installed to comply with 210.70(A)(2)(3), there are other methods that could be used to comply with that section. As others have said, there is no requirement in the NEC...
  4. Replies
    5$$
    Views
    443

    Maybe a "TIA" (Tentative Interim Amendment) but I...

    Maybe a "TIA" (Tentative Interim Amendment) but I don't see one that would require the higher amperage receptacles in a dwelling unit garage to have GFCI protection.
  5. Replies
    12$$
    Views
    852

    One code cycle, I think in the 90s, had...

    One code cycle, I think in the 90s, had underground duct bank ampacities for under 600 volt systems. They were put in the code with an effective date of 3 years later. The action on the next code...
  6. It appears to me that the conductor in question...

    It appears to me that the conductor in question would be a supply side bonding jumper and not an EGC. If that is the case the conductor in each raceway would only need to be a 1/0. See 250.102 and...
  7. Replies
    7$$
    Views
    474

    Unless the pin adapter has a pin made of a class...

    Unless the pin adapter has a pin made of a class B or C stranded conductor, the mechanical lugs are not typically listed as being suitable for a pin adapter. I don't see any real world issue, just a...
  8. Replies
    22$$
    Views
    1,422

    The grounding connection of a cable TV...

    The grounding connection of a cable TV installation around here is on the line side of the demarc and not subject to the rules in the NEC. Even if it were subject to such rules, there is no...
  9. Replies
    16$$
    Views
    892

    "CE" is not a listing. A "listing" requires a...

    "CE" is not a listing. A "listing" requires a third party evaluation. CE is a manufacturer's self evaluation.
  10. In general, my opinion it that insulation tests...

    In general, my opinion it that insulation tests for under 600 volt systems are worthless unless the conduit is wet or contaminated. If there is bare copper, it will pass the megger test unless there...
  11. Replies
    22$$
    Views
    1,422

    They are utilities and not subject to the rules...

    They are utilities and not subject to the rules in the NEC. 90.2(B)(4)
  12. Replies
    22$$
    Views
    1,422

    There is no requirement that the communications...

    There is no requirement that the communications utility use the intersystem bonding point that the electrician is required to install.
  13. It doesn't matter even a little bit where they...

    It doesn't matter even a little bit where they are placed in the panel. In most dwelling units the biggest source of voltage drop when large loads are started is the utility transformer.
  14. Replies
    45$$
    Views
    2,535

    Any one who has been an NFPA member for at least...

    Any one who has been an NFPA member for at least 180 days and wants to physically attend the meeting can vote on the CAMs as well as the complete document.

    The rules can be found at...
  15. Even in metal conduit, unless you have damp or...

    Even in metal conduit, unless you have damp or wet contamination, you can have exposed bare copper and pass a megger test.
  16. Replies
    45$$
    Views
    2,535

    I am not aware of any specific rule that would...

    I am not aware of any specific rule that would require water heaters to have GFCI protection, unless they are cord and plug connected.
  17. Replies
    45$$
    Views
    2,535

    All of the Certified Amending Motions that passed...

    All of the Certified Amending Motions that passed at the technical session go back the the CMPs, and have to be approved by a 2/3s vote of the panel members, and then, it goes to the Standards...
  18. Replies
    25$$
    Views
    2,251

    For equipment that runs at or near full load...

    For equipment that runs at or near full load 24/7, you can often get a 2-3 year payback by increasing the conductor one size, assuming that does not also require a larger conduit.
  19. Replies
    6$$
    Views
    700

    If it is PVC I have no issues with it being...

    If it is PVC I have no issues with it being installed above the frost line. There is no code rule, but I don't like to see rigid or concrete encased PCV above the frost line. I have replaced...
  20. Replies
    24$$
    Views
    1,774

    I expect that they have not revised their...

    I expect that they have not revised their information since the 2017 came out. The requirement for the countertop listing requires that the device pass a liquid spill test in both the up and seated...
  21. Replies
    24$$
    Views
    1,774

    The only pop up currently on the market that...

    The only pop up currently on the market that complies with 406.5(E) in the 2017 code for countertop receptacles in the one made by Hubbell. If you are on the 2014, the rules were different and a...
  22. Replies
    6$$
    Views
    422

    You need to test from the electrical system...

    You need to test from the electrical system grounding electrode to "remote earth", often defined as being at least 50' from any grounding electrode or metallic object that is connected to the...
  23. Replies
    18$$
    Views
    1,104

    The smoke alarms are covered Chapter 29 of NFPA...

    The smoke alarms are covered Chapter 29 of NFPA 72. 29.9.4(5) permits such systems to be supplied by an AFCI or GFCI protected branch circuit as long as the smoke alarm has a secondary power source....
  24. You need to take a look at Article 630 for...

    You need to take a look at Article 630 for conductor and OCPD sizing for welders.
  25. Replies
    20$$
    Views
    2,770

    40% fill of 1" rigid is 4.85 of the 0.305...

    40% fill of 1" rigid is 4.85 of the 0.305 diameter cables.