    Every bender has it's own quirks. The first...

    Every bender has it's own quirks.

    The first thing you should do with a new bender is run some test pieces through it and adjust your measurements and deducts accordingly.

    The only person that...
  2. Replies
    7$$
    Views
    254

    As long as you can pull it out and put it back...

    As long as you can pull it out and put it back the way it should look with the factory deadfront covers, etc, then I don't see the problem.

    I don't see it as any different than a regular...
  3. Replies
    31$$
    Views
    784

    I don't see the problem? Install the nonfused...

    I don't see the problem?

    Install the nonfused "utility" disconnect. Bond the enclosure to the grounded conductor just like you would any piece of equipment upstream from a service disconnect. ...
  4. Thread: Tap Rule Question

    by Cow
    Replies
    7$$
    Views
    313

    The only thing I could possibly see, is that you...

    The only thing I could possibly see, is that you have two service disconnects. They would need to be grouped. And the wiring ahead of the split bolts would need to be sized to carry the calculated...
  5. Thread: VFD cable types

    by Cow
    Replies
    7$$
    Views
    426

    I've never heard mention of requirements for the...

    I've never heard mention of requirements for the input wiring to a vfd needing to be a certain type. I have heard of vfd output wiring needing to be a certain type.
  6. Replies
    16$$
    Views
    712

    I would do everything in my power to talk them...

    I would do everything in my power to talk them into a subpanel, rather than hooking a bunch of 120v and 240v receps to the same circuit.
  7. Thread: southwire product

    by Cow
    Replies
    2$$
    Views
    320

    Read 336.12(2).

    Read 336.12(2).
  8. Replies
    6$$
    Views
    279

    Like Tom said, you really need to talk to your...

    Like Tom said, you really need to talk to your suppliers.

    I've went through the catalogs before looking for similar, but there are so many variations, it's easy to go off the rails and miss one...
  9. Replies
    17$$
    Views
    1,029

    The simplest is to choose not to do business with...

    The simplest is to choose not to do business with them again. It's not unreasonable to think if they asked you for a price, you should get a fair shake at actually getting the project if you're the...
  10. Replies
    11$$
    Views
    457

    That is one long tap!!!! Without looking it...

    That is one long tap!!!!

    Without looking it up, you may be able to get away with it outside, but not in a building.
  11. 1600' between pull points a long time ago for an...

    1600' between pull points a long time ago for an irrigation pivot. Now it's all cablecon.

    A few times a year we'll do 750-1200' footers with no pull points in the middle. Really no different...
  12. It's all relative. But with few details given,...

    It's all relative.

    But with few details given, it's hard to know....
  13. Thread: AB140m

    by Cow
    Replies
    24$$
    Views
    1,225

    I'm told it's affects the devices trying to read...

    I'm told it's affects the devices trying to read the cows ear tags. The VFD and output wiring are basically like a giant FM antenna that cause interference issues. The closer the VFD and shorter...
  14. Thread: AB140m

    by Cow
    Replies
    24$$
    Views
    1,225

    If you're putting these in a dairy, it gets tough...

    If you're putting these in a dairy, it gets tough with EMF if they're using RFID ear tags on the cows.

    We've been doing them lately with Lenze ACTech Nema4X VFD's right on the fan with a short...
  15. Thread: VFD's Tripping

    by Cow
    Replies
    18$$
    Views
    1,080

    For what you've described, a line reactor can...

    For what you've described, a line reactor can only help.

    I've started installing 3% TCI KDR style reactors on a good majority of VFD's now. I prefer TCI's lineup over MTE's, just for reason that...
  16. No.

    No.
  17. Replies
    8$$
    Views
    457

    Install a j-box/gutter/etc adjacent to the...

    Install a j-box/gutter/etc adjacent to the disconnect. Run full sized 100 amp wire from the disco to the j-box/gutter/etc and tap the #6's and 10's to that.
  18. Replies
    36$$
    Views
    2,577

    We don't ask for money up front, even on large...

    We don't ask for money up front, even on large projects. We do progress bill monthly.

    For some residential customers that seem a little questionable, we will ask for 50% upfront. This is very...
  19. Thread: Split-bus panels

    by Cow
    Replies
    11$$
    Views
    562

    If the panel is in good shape, no, I do not...

    If the panel is in good shape, no, I do not recommend they replace it.

    The only wear items are the breakers themselves. And those can be replaced.
  20. Replies
    3$$
    Views
    216

    Heavy loads near the main breaker/lugs, if...

    Heavy loads near the main breaker/lugs, if possible.

    Other than that, whatever makes sense when you walk up to the panel and need to work on it or find a breaker. I like to group areas of the...
  21. Replies
    13$$
    Views
    669

    Are you able to use 310.15(A)2 & Exc?

    Are you able to use 310.15(A)2 & Exc?
  22. Thread: Fired up.

    by Cow
    Replies
    18$$
    Views
    1,005

    It wouldn't be an issue here. I ran a feeder...

    It wouldn't be an issue here.

    I ran a feeder in a home once from the main panel to a sub I installed in the garage. The homeowner would take it from there with the BC's. Inspector made a note,...
  23. Thread: Motor Disconnect

    by Cow
    Replies
    7$$
    Views
    365

    The disconnects I've replaced did not appear to...

    The disconnects I've replaced did not appear to be cycled very often, they were maintenance disconnects. Every one of them started getting hot right where the knife blades rock into their holders.
  24. Thread: Motor Disconnect

    by Cow
    Replies
    7$$
    Views
    365

    I wouldn't do it. Disconnect switches lead...

    I wouldn't do it.

    Disconnect switches lead much shorter lives when they are loaded that heavy in my experience. Whether following manufacturer ratings or not.
  25. Replies
    7$$
    Views
    393

    Can you go six wide instead of 2x3? The...

    Can you go six wide instead of 2x3?

    The spacers are a necessity when you stack them, as is flowable fill or CDF to get the compaction you need around and between the conduits. If they don't like...