  1. Replies
    7$$
    Views
    356

    If there is a door that can close between those...

    If there is a door that can close between those spaces, you'll never meet the audibility/intelligibility requirements. On the other hand, NFPA 72 in Section 24.4.1.2.2.4 specifically exempts certain...
  2. Replies
    15$$
    Views
    381

    When I worked for a contractor, my techs would...

    When I worked for a contractor, my techs would take the power for the shunt (if we used one) from the device being shutdown. If the power failed, no worries, because the equipment was off already.
    ...
  3. Replies
    6$$
    Views
    259

    The AC could be through-the-wall split units.

    The AC could be through-the-wall split units.
  4. Replies
    7$$
    Views
    356

    See Annex D for acceptable test methods. Most...

    See Annex D for acceptable test methods. Most commonly, it's the AHJ walking around and saying "push it up in this area" or "a little too loud here". And that's fine by NFPA 72.
  5. Replies
    7$$
    Views
    356

    You know, I didn't read it that way. :slaphead: ...

    You know, I didn't read it that way. :slaphead: IFF that's the case, then you will definitely not meet the intelligibility requirements if the notification appliance is in the main room and the...
  6. Replies
    7$$
    Views
    356

    With the product offerings available from all the...

    With the product offerings available from all the major players you shouldn't have any issue getting intelligibility in a bathroom, unless you can't tap down to 1/8 watt. Anything higher is likely...
  7. Standard 2-wire heat detectors are not listed to...

    Standard 2-wire heat detectors are not listed to be installed with smoke alarms. How would that work even in concept? A fire alarm panel circuit is designed to accept a shorting device as an input...
  8. "Standard for the Installation of Lightning ...

    "Standard for the
    Installation of Lightning
    Protection Systems"
  9. Replies
    8$$
    Views
    1,012

    This is really the fire inspector's thing to...

    This is really the fire inspector's thing to worry about. Were I he, at the third time I came in and saw this it would be a $500 fine, or whatever maximum for the third offense is, and use whatever...
  10. Hydraulic pumps may incorporate an internal...

    Hydraulic pumps may incorporate an internal pressure relief that limits output pressure. If you could grab a model number that would be very helpful.
  11. Replies
    22$$
    Views
    995

    I'll repeat my earlier objection; we don't know...

    I'll repeat my earlier objection; we don't know the OP is dealing with multiple dwellings. We shouldn't bother arguing this point until we have this information.
  12. Replies
    8$$
    Views
    1,091

    That's what I was thinking, unless the project...

    That's what I was thinking, unless the project spec calls for a separate pipe for one of them. The Port Authority of NY/NJ is famous for this.
  13. Replies
    17$$
    Views
    1,174

    See "condensation" and "bang-o" in the OP.

    See "condensation" and "bang-o" in the OP.
  14. Replies
    20$$
    Views
    1,999

    I'm with you on that. Also, since this is all...

    I'm with you on that.

    Also, since this is all low voltage, article 300 requirements, including conduit fill don't apply, right?
  15. Replies
    22$$
    Views
    995

    Have we established that this is a multi-family...

    Have we established that this is a multi-family dwelling, since that's what 220.84 is all about?
  16. Replies
    14$$
    Views
    795

    We have a couple of cabinets in our bathroom,...

    We have a couple of cabinets in our bathroom, just run-of-the-mill stuff. I know that after a shower, if you open them up you'll find a very fine film of condensate on the objects inside the...
  17. Replies
    7$$
    Views
    547

    That will depend on jurisdiction. I know that it...

    That will depend on jurisdiction. I know that it isn't true in NJ.
  18. Replies
    7$$
    Views
    547

    I wouldn't try to integrate them. Too many...

    I wouldn't try to integrate them. Too many moving parts in the design. Don't forget, you have to monitor the source for each shunt coil at the fire alarm panel. Anyone on staff familiar with...
  19. Thread: UPS

    by gadfly56
    Replies
    9$$
    Views
    514

    Those categories are in ascending order of cost. ...

    Those categories are in ascending order of cost. If the bean-counters had any major input to the selection process, count on them having moved heaven and earth for the cheapest solution. If the...
  20. The AHJ is the final word, of course, but the...

    The AHJ is the final word, of course, but the fact that you are matching existing work should lean towards being compliant in your jurisdiction.
  21. Replies
    7$$
    Views
    481

    Ahhhhh, when you said "tenant" I automatically...

    Ahhhhh, when you said "tenant" I automatically thought "dwelling unit". :slaphead: In that case, I'll change my "no" to a "yes".
  22. Replies
    7$$
    Views
    481

    I'd suggest the relevant rule is 210.25(A): ...

    I'd suggest the relevant rule is 210.25(A):

    210.25 Branch Circuits in Buildings with More Than
    One Occupancy.

    (A) Dwelling Unit Branch Circuits. Branch circuits in
    each dwelling unit shall...
  23. Replies
    7$$
    Views
    481

    1. Yes. 2. No.

    1. Yes.
    2. No.
  24. Replies
    7$$
    Views
    547

    If the elevator is already connected through a...

    If the elevator is already connected through a shunt trip breaker which already connects to the fire alarm panel, there is nothing further to do. It appears someone may have asked you to install a...
  25. Replies
    7$$
    Views
    768

    I went there and to Mark's blog as well. All I...

    I went there and to Mark's blog as well. All I can say is, lots of luck, ggunn, you're going to need it.