514.11 a and c

Status
Not open for further replies.

pjg

Member
Can the required disconnect in this artcle be a non fused 3R "swing arm" 2 pole disconnect(properly labeled) that will open the hot and the neutral vs. a 3R mushroom stop button?

I realize the AHJ has the call, but I'm curious what other electricians think.

The job I am looking at is an above ground 500 gal. gasoline tank with two dispensers being fed with one 120 volt circuit.

thanks for your thoughts
 

physis

Senior Member
I don't have an ounce of experience with classified but I don't see anything wrong with what you intend to do based on the code (not that I know much in this area). All due lack of respect for myself, you should wait to hear from someone more knowlegable than me.

Why do you think the AHJ makes the call? He can only enforce the NEC and local ordinances.
 

SEO

Senior Member
Location
Michigan
Section 514.11 (C) is for unattended self-service motor fuel dispensing facilities. If this is the case per this section a disconnect may comply. The question, is a disconnect an emergency control? Only your AHJ can make the call.
 