Section/Paragraph: 220.14(H)
Deleted Text
220.14 Other Loads ? All Occupancies.
....
(H) Fixed Multioutlet Assemblies.
....
(1) Where appliances are unlikely to be used simultaneously, each 1.5 m (5 ft) or fraction thereof of each separate and continuous length shall be considered as one outlet of not less than 180 volt-amperes.
(2) Where appliances are likely to be used simultaneously, each 300 mm (1 ft) or fraction thereof shall be considered as an outlet of not less than 180 volt-amperes.
Substantiation:
"thereof" is an archaic term which is considered to reduce clarity according to NEC_StyleManual_2011.pdf 3.3.4.