    Continuous GEC from Ground Rod to Water

    On a new 200amp service, Does the grounding electrode conductor have to be unspliced from the panel to the ground rod and to the water pipe within 5' of the water entrance to the house? Every section I read says it only needs to be unspliced to the most convieniant electrode, then bonding jumpers to all of the other electrodes. If the water line is 100' away, can't I just go to the driven ground rod 1st and then add another clamp to the water line? Everyone in my office says this has to be continous through all electrodes with no splices except for welding or irreversible clamps. Thanks Everyone!!

  2. #2
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,657
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    You are correct, see this on going thread.

    Roger
    Moderator

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,245
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The GEC can end at the first electrode. From there you may join other electrodes with bonding jumpers. If you had a building with building steel bonded at the service and a water pipe 300' away you could just bond the water pipe to the building steel with a bonding jumper. The GEC is the conductor between the neutral and the electrode itself it does not need to continue unbroken to any other electrodes.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Apr 2003
    Location
    Planet macmikeman
    Posts
    3,491
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If your water pipe is 300 feet away, chances are pretty good that its not inside the building we are talking about here, in which case the 5' rule doesn't apply either . 250.52
    85deg. an Sunny today.

  5. #5
    Join Date
    Sep 2009
    Location
    Hesperia,CA
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Talking

    Thanks for all of the info!! you guys are the best!! ::grin:

  6. #6
    Join Date
    Mar 2004
    Location
    Arizona
    Posts
    3,913
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by macmikeman View Post
    in which case the 5' rule doesn't apply either . 250.52
    I don't understand why not ?
    Frank Arizona,USA

  7. #7
    Join Date
    Apr 2003
    Location
    Planet macmikeman
    Posts
    3,491
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by benaround View Post
    I don't understand why not ?
    Did you read the code reference I gave? I'll elaborate, first word of the second sentance of 250.52. It is almost universal in overlooked when this code is read.