Is this device grounded?

Learn the NEC with Mike Holt now!

Is this device grounded?


  • Total voters
    97
Status
Not open for further replies.

e57

Senior Member
From another thread, and a pet peeve of mine, I bring you a poll....

Is this device grounded?

attachment.php



If it is not grounded - under what conditions could it be grounded?
If it is grounded - state a code ref...
If it is not grounded - state a code ref...
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
404.9(B)(1) doesn't ask for anything more than metal screws. I say the metal yoke is grounded.
 

e57

Senior Member
But, but, but....

'What about 404.9(B)1? It's 'mounted' to a metal box with metal screws???? :confused:'

But, but, but....

'It's easier this way.... and the code says....'

But, but, but....

'What if the screws were tighter?'


IMPO it's really not "mounted" - to anything...
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
What is the device yoke "mounted" to?

The words "firmly secured" are clearly describing the word "mounting" - nothing in the picture is "firmly secured" to anything, and if it were - it would be secured to sheet-rock - not the metal box...
I'll agree that the diagram shows an incomplete installation.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Here's the Code
2008 NEC

404.9 Provisions for General-Use Snap Switches.

(B) Grounding.
Snap switches, including dimmer and similar control switches, shall be connected to an equipment grounding conductor and shall provide a means to connect metal faceplates to the equipment grounding conductor, whether or not a metal faceplate is installed. Snap switches shall be considered to be part of an effective ground-fault current path if either of the following conditions is met:
(1) The switch is mounted with metal screws to a metal box or metal cover that is connected to an equipment grounding conductor or to a nonmetallic box with integral means for connecting to an equipment grounding conductor.
 