Egc

Status
Not open for further replies.

SAP

Senior Member
Location
Fresno Ca
Micro inverters, I've always wire nutted my EGC when it was easier using a crimp sleeve, I got called on using wire nuts on a enphase system. AHJ said they want them irreversible crimped, I tried to find it in code were it states the the EGC has to be irreversible crimped, can someone give me a code reference were it says it does not, thanks
 
A GEC needs an irreversable crimp/splice method, but not an EGC. I have no idea if solar has some funny rule I do not know about.

Why GEC is more important than EGC (since requiring irreversible crimp implies this)? Isn't it both are required to protect lives and structures (fire)? I would think irreversible crimp required in both case makes sense.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Why GEC is more important than EGC (since requiring irreversible crimp implies this)? Isn't it both are required to protect lives and structures (fire)? I would think irreversible crimp required in both case makes sense.
A case could be made that a EGC is more important. Why the irreversible crimp for the GEC? No good reason other than the warm fuzzies people get when they connect a wire to earth.
 