cppoly

Senior Member
Location
New York
A SOOW cable 16-5 has power conductors and data conductors in the same cable. Are these conductors required to be separated by a voltage barrier if they enter a junction box?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A SOOW cable 16-5 has power conductors and data conductors in the same cable. Are these conductors required to be separated by a voltage barrier if they enter a junction box?
If they are permitted to be in the same cable, why would separation be required in a junction box?
 

cppoly

Senior Member
Location
New York
My thoughts exactly but didn't want to clutter up my question.

But my follow up question is, I thought data and power had to be separated so how are they permitted to be in the same cable?
 

JFletcher

Senior Member
Location
Williamsburg, VA
A SOOW cable 16-5 has power conductors and data conductors in the same cable. Are these conductors required to be separated by a voltage barrier if they enter a junction box?

Take a look at 800.133(A)(1)(b) exception. Are the power conductors part of a class 2 or 3 circuit?

I dont see how you could bring a single cable thru a KO/fitting and split it in the box when the dividers completely transect the box into two halves...
 

iwire

Moderator
Staff member
Location
Massachusetts
A SOOW cable 16-5 has power conductors and data conductors in the same cable. Are these conductors required to be separated by a voltage barrier if they enter a junction box?

What is the application?

In other words does the NEC apply to this installation?
 