code violation?

Status
Not open for further replies.

dreamsville

Senior Member
Location
Michigan
Was in the mall this morning. Saw this cord going down through the wood chips in the top of a raised walkway divider in the center of the mall. So I dug down and found this.

What do you think? I think there exists a code section that would prohibit this. I had to dig down 3 inches to uncover it. The GFCI receptacle was facing up underneath the wood chips with an extension cord plugged in. Not sure where the other end of the cord was feeding to, it disappeared beneath the chips...

View attachment 4369
 

Volta

Senior Member
Location
Columbus, Ohio
You might be able to try 110.11, if the mulch dust could deteriorate the GFCI.

You might try 314.27(C), but that area is not designed for walking, so may not be a floor . . .

Or you might try 400.8(5), but again, the mulch may not be considered a "floor".
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
You might be able to try 110.11, if the mulch dust could deteriorate the GFCI.

You might try 314.27(C), but that area is not designed for walking, so may not be a floor . . .

Or you might try 400.8(5), but again, the mulch may not be considered a "floor".

Keep fishing. :D
 

iwire

Moderator
Staff member
Location
Massachusetts
110.12(C).

IMO the internal parts are being contaminated by abrasives.

attachment.php
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Let's take this away from the mall and put it in someones residence, and let's assume there is a violation, who would be the party that could site a violation?

Roger
 

iwire

Moderator
Staff member
Location
Massachusetts
You mean (B)?

No C, but I am looking at my 2005. :)

What if it's a TR receptacle?

Then I would say that the abrasives adversely effect the operation of the tamper shutters.

If I am the inspector I believe that is a judgment call I could make based on the wording in 110.12(C) or I guess (B) in the 2008.

Or I could just mention it to the fire dept and they would have it fixed that day. :grin:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
So what control would an elecrician or inspector have over what happens after the C.O.? This could be compared with why article 210.21(B)(2) is waste of ink.

When an end user decides to do something it's going to happen.

Roger
 