NEC 220.1 Load Calculations

Status
Not open for further replies.

KMeni

Member
Does the NEC Code recognize Power Monitoring using Testing Equipment as way to collect data for calculating existing electrical system loads.
 

iwire

Moderator
Staff member
Location
Massachusetts
Without me lookiing, doesn't it allow if it's there recording for 30 days?

It looks like they would rather have the demand data for one year but if not available you can use a meter.

(1) The maximum demand data is available for a 1-year
period.


Exception: If the maximum demand data for a 1-year period
is not available, the calculated load shall be permitted
to be based on the maximum demand (measure of average
power demand over a 15-minute period) continuously recorded
over a minimum 30-day period using a recording
ammeter or power meter connected to the highest loaded
phase of the feeder or service, based on the initial loading
at the start of the recording. The recording shall reflect the
maximum demand of the feeder or service by being taken
when the building or space is occupied and shall include by
measurement or calculation the larger of the heating or
cooling equipment load, and other loads that may be periodic
in nature due to seasonal or similar conditions.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
220.87 in the 2005, may be relocated in the 2008.

Same place.

Without me lookiing, doesn't it allow if it's there recording for 30 days?

Not bad for not looking.

220.87 Determining Existing Loads.

The calculation of a feeder or service load for existing installations shall be permitted to use actual maximum demand to determine the existing load under all of the following conditions:

(1) The maximum demand data is available for a 1-year period.

Exception: If the maximum demand data for a 1-year period is not available, the calculated load shall be permitted to be based on the maximum demand (measure of average power demand over a 15-minute period) continuously recorded over a minimum 30-day period using a recording ammeter or power meter connected to the highest loaded phase of the feeder or service, based on the initial loading at the start of the recording. The recording shall reflect the maximum demand of the feeder or service by being taken when the building or space is occupied and shall include by measurement or calculation the larger of the heating or cooling equipment load, and other loads that may be periodic in nature due to seasonal or similar conditions.

(2) The maximum demand at 125 percent plus the new load does not exceed the ampacity of the feeder or rating of the service.

(3) The feeder has overcurrent protection in accordance with 240.4, and the service has overload protection in accordance with 230.90.
 

iwire

Moderator
Staff member
Location
Massachusetts
Notice this part.


220.87 Determining Existing Loads.

The calculation of a feeder or service load for existing installations shall be permitted to use actual maximum demand to determine the existing load under all of the following conditions:

(1) The maximum demand data is available for a 1-year period.

Exception:If the maximum demand data for a 1-year period is not available, the calculated load shall be permitted to be based on the maximum demand (measure of average power demand over a 15-minute period) continuously recorded over a minimum 30-day period using a recording ammeter or power meter
connected to the highest loaded phase of the feeder or service, based on the initial loading at the start of the recording. The recording shall reflect the maximum demand of the feeder or service by being taken when the building or space is occupied and shall include by measurement or calculation the larger of the heating or cooling equipment load, and other loads that may be periodic in nature due to seasonal or similar conditions.

(2) The maximum demand at 125 percent plus the new load does not exceed the ampacity of the feeder or rating of the service.

(3) The feeder has overcurrent protection in accordance with 240.4, and the service has overload protection in accordance with 230.90.

This tells me I would not have to use a fancy three or four channel recording meter but a much less expensive single channel meter. :)
 