Reinholds PA
Hi,
I am currently bidding a control job for an HVAC contractor, in the spec section for installation of HVAC controls it states to install concealed wiring in a raceway. The building is 3-story wood frame retirement home. Does anyone have experience in this building type and ever see raceways for all the low-voltage control wiring?
 

JFletcher

Senior Member
Location
Williamsburg, VA
Welcome. Never seen this required, but if it is in the job spec, bid it accordingly. If it doesnt spec the raceway type, ENT is fairly easily fishable, tho surface mount EMT would probably be the cheapest solution if allowed.

You may want to put in an RFI as those specs could be duplicated from another project.
 