    Question Wiring 277V Lighting

    I realize that 277V is derived from a 3-phase Y transformers' line-line voltage (480V/1.732). So, my way of thinking is that if you draw a 3-phase Y transformer, you would connect your load (in this case lighting) say from a-phase to b-phase. But that is not the case, there are not 2 phases there, there is instead a hot and a neutral. Where did the neutral come from? How is 277V lighting wired? And why is it dangerous to work on energized 277V lighting circuits?

  2. #2
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,032
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by alittleee View Post
    I realize that 277V is derived from a 3-phase Y transformers' line-line voltage (480V/1.732). So, my way of thinking is that if you draw a 3-phase Y transformer, you would connect your load (in this case lighting) say from a-phase to b-phase. But that is not the case, there are not 2 phases there, there is instead a hot and a neutral. Where did the neutral come from? How is 277V lighting wired? And why is it dangerous to work on energized 277V lighting circuits?
    The source would be 480 Wye not 480 delta and you would have 480 line to line and 277 from any line to neutral.

    This is no different than 208Y/120 ..... other than the voltage itself.

  3. #3
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,578
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Name:  wye_detail1.jpg
Views: 29541
Size:  12.4 KBAttached may help

    and
    It's dangerous to work on any energized circuits (and a violation except in extreme circumstances)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  4. #4
    Join Date
    Feb 2007
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Red face sorry

    I am sorry. I was just getting ready to argue with you and I was typing out the "formula" and realized I was thinking just bass ackward. Line voltage is higher than phase voltage in Y connections. Sorry to waste your time. But - it made me think strait by trying to argue with you anyway.

  5. #5
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,578
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by alittleee View Post
    I am sorry. I was just getting ready to argue with you and I was typing out the "formula" and realized I was thinking just bass ackward. Line voltage is higher than phase voltage in Y connections. Sorry to waste your time. But - it made me think strait by trying to argue with you anyway.
    Go ahead and argue ,To quote G B Shaw:

    I learned long ago, never to wrestle with a pig. You get dirty, and besides, the pig likes it.
    George Bernard Shaw
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •