communication pul box

Status
Not open for further replies.

jjavier

Member
Location
Maine
In the communication pull box with one conduit 2"pvc, is it the same rule 6*2 = 12" minimum dimension than electric boxes?
 

Carultch

Senior Member
Location
Massachusetts
In the communication pull box with one conduit 2"pvc, is it the same rule 6*2 = 12" minimum dimension than electric boxes?

That rule is specific to #4 and larger conductors. I don't think you'll have a communication cable that large. In any case, you still do need to plan for proper bend radius.
 