    Shielded 600V Feeder Cable

    Does anyone have any information on why it would be advantageous to install shielded feeder cable to the incoming AC section on a VFD lineup vs non-shielded? Or if braided straps would stop harmonics from polluting up the line. I can understand using it for the load side of the VFD but do not understand, fully, for the line side prior the filter, which already contains an isolation transformer.
    I just can't fathom the reasoning behind it, especially since 3c/750 w/g shld is around 80 dollars a foot. Then again I am not an engineer.
    Thanks in advance.

  2. #2
    Join Date
    Jun 2010
    Posts
    1,928
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Breaker19 View Post
    Does anyone have any information on why it would be advantageous to install shielded feeder cable to the incoming AC section on a VFD lineup vs non-shielded? Or if braided straps would stop harmonics from polluting up the line. I can understand using it for the load side of the VFD but do not understand, fully, for the line side prior the filter, which already contains an isolation transformer.
    I just can't fathom the reasoning behind it, especially since 3c/750 w/g shld is around 80 dollars a foot. Then again I am not an engineer.
    Thanks in advance.
    Running the cables in grounded EMC already provides excellent shielding.

  3. #3
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,656
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The idea behind shielding is to prevent the cables from becoming radio transmitting antennae. If you are laying them in tray, shielding is a must. If pulling them in grounded conduit, as Electric-Light said the conduit serves the same function. Pulling shielded cable inside of grounded conduit is a waste IMHO.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  4. #4
    Join Date
    Jun 2007
    Location
    Ohio
    Posts
    559
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Jraef is correct. Two engineers from Belden and one from Rockwell wrote a paper about this that was presented at the 1999 IEEE PCIC conference. It's one of the best papers out there on VFD cabling - this feeder cable antenna effect is just one of a number of topics covered. They also discuss the life expectancy of various cable insulations under years of reflected wave voltage pulses - this is the only place I've seen any serious analysis on VFD cable life.