    Feeder Grounded Conductor Minimum Size

    2011 NEC 215.2(A)(2) appears to refer to itself. "Additional minimum sizes shall be as specified in 215.2(A)(2)..."

    Can anyone explain that reference?
    e^(i pi) = -1

  2. #2
    Join Date
    May 2007
    Location
    Baton Rouge
    Posts
    770
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The grounded conductor can be no smaller than the EGC so as to allow it to carry fault current.
    Jason

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,737
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    215.2(A)(2) is pretty clear. The grounded conductor (neutral) shall not be smaller than the egc from T. 250.122. Thus a 100 amp feeder would need a neutral sized at #8. Remember if the feeder doesn't require a neutral then one is not required. If you decide to pull one for future use then it cannot be smaller than the egc, as Walker stated above.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky