    MC cable & grounding. Tail to the box & receptacles?

    12/2 MC cable in a 5" box.
    You take the green wire & secure it to the box with a green ground screw. Thus grounding the box.

    Do you also need to bring a tail to the ground screw of a duplex receptacle?

    If yes, why? If the box is grounded, then so is the receptacle through the 6/32 screws. Or alternately, if the receptacle is grounded, then the box is grounded through the 6/32's.

    I'm feeding a 5" box for quad receptacles plus 2 12/2 jumpers to other boxes. I end up with 6 grounds under a wire nut.

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,329
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The 6-32 screws alone are not permitted to ground the receptacle. The device would need a bonding jumper or must be a self grounding receptacle. Also you cannot connect the EGC to the device and ground the metallic box through the device.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    The 6-32 screws alone are not permitted to ground the receptacle. The device would need a bonding jumper or must be a self grounding receptacle. Also you cannot connect the EGC to the device and ground the metallic box through the device.
    If this is a metal box that has the EGC bonded to it, wouldn't a regular receptacle with the plastic washers removed and metal to metal ( yoke to box) be okay?
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #4
    Join Date
    Aug 2010
    Posts
    11
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I meant self-grounding receptacles.

    That's always been good enough with Bx. The jacket of the Bx bonding the box & the 6/32's grounding the receptacle.
    So why not with MC cable?

    I know I'm conflating 'bonding' & 'grounding' but that's a whole other issue with it's own section of the forum.

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,329
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    If this is a metal box that has the EGC bonded to it, wouldn't a regular receptacle with the plastic washers removed and metal to metal ( yoke to box) be okay?

    Not for the box he's using.


    Quote Originally Posted by Sir String View Post
    I meant self-grounding receptacles.

    That's always been good enough with Bx. The jacket of the Bx bonding the box & the 6/32's grounding the receptacle.
    So why not with MC cable?

    I know I'm conflating 'bonding' & 'grounding' but that's a whole other issue with it's own section of the forum.

    If the receptacle is self grounding you can use it without a bonding jumper for either AC or MC to a grounded metal box. If it's not self grounding you need a bonding jumper for either of those wiring methods.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,782
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If you switched to MCap and self grounding receps, you wouldn't have to splice any grounds.

  7. #7
    Join Date
    Sep 2004
    Location
    Durham, NC
    Posts
    5,500
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Cow View Post
    If you switched to MCap and self grounding receps, you wouldn't have to splice any grounds.
    Better get more wire...

    Third sentence in 250.64, + ...shall apply at each end... between cabinet or equipment... continually
    If you are even thirsty, you are two quarts low.

  8. #8
    Join Date
    Jul 2010
    Location
    Great NW
    Posts
    182
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sir String View Post
    12/2 MC cable in a 5" box.
    You take the green wire & secure it to the box with a green ground screw. Thus grounding the box.

    Do you also need to bring a tail to the ground screw of a duplex receptacle?

    If yes, why? If the box is grounded, then so is the receptacle through the 6/32 screws. Or alternately, if the receptacle is grounded, then the box is grounded through the 6/32's.

    I'm feeding a 5" box for quad receptacles plus 2 12/2 jumpers to other boxes. I end up with 6 grounds under a wire nut.
    I'd go with406.3(C)
    The EGC contacts of a recept... shall be grounded by connection to the EGC of the circuit supplying the recept.

    The branch circuit wiring method shall include or provide an EGC to which the EGC contact(s) of the recept. are connected

    406.3 D,1 points to that too. But I don't know what you mean by 5" box. Is that a 4 and 11/16" ?
    Fixing shorts for money

  9. #9
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,875
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    If this is a metal box that has the EGC bonded to it, wouldn't a regular receptacle with the plastic washers removed and metal to metal ( yoke to box) be okay?
    Why is that the way you have been doing it. You need to use those receps with the brass clip and are considered self grounding. for this purpose.

  10. #10
    Join Date
    Aug 2010
    Posts
    11
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Finite10 View Post
    ...But I don't know what you mean by 5" box. Is that a 4 and 11/16" ?
    Yes, of course.