90.7 Examination of Equipment for Safety.
.....................
...It is the intent of this Code that factory-installed internal wiring or the construction of equipment need not be inspected at the time of installation of the equipment, except to detect alterations or damage, if the equipment has been listed by a qualified electrical testing laboratory that is recognized as having the facilities described in the preceding paragraph and that requires suitability for installation in accordance with this Code.......
We are having different views on how the inspector community interprets this.
Since one of our HVAC product lines is UL listed & label, will an inspector typically look at the internal, factory installed wiring?
Typical wiring is a few lights, VFD to fan motors and service receptacle. There are special cases where a N.F. motor disconnect will be installed.
Thanks for any comments
.....................
...It is the intent of this Code that factory-installed internal wiring or the construction of equipment need not be inspected at the time of installation of the equipment, except to detect alterations or damage, if the equipment has been listed by a qualified electrical testing laboratory that is recognized as having the facilities described in the preceding paragraph and that requires suitability for installation in accordance with this Code.......
We are having different views on how the inspector community interprets this.
Since one of our HVAC product lines is UL listed & label, will an inspector typically look at the internal, factory installed wiring?
Typical wiring is a few lights, VFD to fan motors and service receptacle. There are special cases where a N.F. motor disconnect will be installed.
Thanks for any comments