How do you bond the metallic box that the IG receptacle is attached to?

MC cable terminates at 4" square box . Cable only has 1 insulated equipment ground conductor?

What is used for box bonding?..
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
I bet supply house is more likely to have HCF cable, which the sheath would be acceptable for EGC plus a green conductor inside then they are to have that product on hand.

That is probably true. I have never used MC for IG applications. It's been many years since I have installed IG's. We used to run EMT or flex with 2 EGC's if fishing down walls.
 