IT room bonding question

Status
Not open for further replies.

bluecollar84

Senior Member
Location
US
Can I run a interconnected bonding wire in a already installed 4” conduit with existing communications circuits in it ? If yes or no what code article says so


Sent from my iPhone using Tapatalk
 

Andy Delle

Senior Member
Location
Los Angeles CA
Strictly from an electronics perspective, NEC aside, it depends. What is the bonding wire for? If it's to ground a raised floor or equipment racks, that would be OK. If it's for bonding an CRAC or PDU, I would not mix that with communications wiring. reason is potential noise ingress.
 

bluecollar84

Senior Member
Location
US
It’s from the interconnected bonding terminal bar in the main electric room to the IT room bonding terminal strip with #6 copper wire


Sent from my iPhone using Tapatalk
 