Neutral to lug on panel

Status
Not open for further replies.

ivsenroute

Senior Member
Location
Florida
Can I connect the neutral of a 240v system to a lug that is screwed into the body of the panel frame (inside panel) if it is too short to make it to the neutral bar?

If this is a main panel and not a sub feed:
 

ivsenroute

Senior Member
Location
Florida
Nothing gives. Sometimes people I know check out this board and if I ask a question that they are arguing then see the answer here, they stop arguing.
 

Strife

Senior Member
This sounds like one of those: "if you have to ask, you probably know the answer"?


Can I connect the neutral of a 240v system to a lug that is screwed into the body of the panel frame (inside panel) if it is too short to make it to the neutral bar?

If this is a main panel and not a sub feed:
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I can relate. I tell them, it's just an ole senile inspector babbling.
They read it here, it's gospel.
I often post questions for which I know the answer when I know the job related to a watcher/non-poster
Some don't post as they think they might "look stupid", but since my stupidity is acknowledged, I can post.
 

hotwire1955

Senior Member
Location
nj
Can I connect the neutral of a 240v system to a lug that is screwed into the body of the panel frame (inside panel) if it is too short to make it to the neutral bar?

If this is a main panel and not a sub feed:

yes if the lug is listed for two conductors and the jumper lands on the neutral bar
 

kwired

Electron manager
Location
NE Nebraska
Can I connect the neutral of a 240v system to a lug that is screwed into the body of the panel frame (inside panel) if it is too short to make it to the neutral bar?

If this is a main panel and not a sub feed:


In general I'd say splice the conductor then run the rest of the way to the neutral bar.
 

ivsenroute

Senior Member
Location
Florida
I can relate. I tell them, it's just an ole senile inspector babbling.