Photo of 43B while checking PF. Can you tell by this information what size PFC is needed to correct it to +.9?
(IDK, so this is a B style question vs A.)

Loads are multiple fan motors on a feeder. Individual PFC will not happen but up to four may be a go. One for each group of fans.

Loads are 3phase 480v FWIW. Reflection on right covers the 100A scale
n barn PF.jpg
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
With 29.5 kW, a pf of 0.9 would make the KVA value equal to (29.5)/(0.9), or 32.8. Next step is to find the third leg using Pythagorean formula. KVAR squared equals 32.8 squared minus 29.5 squared, so KVAR equals 14.3. You add 27.6 KVAR of capacitors, and you will get your .9 pf.
 

lielec11

Senior Member
Location
Charlotte, NC
With 29.5 kW, a pf of 0.9 would make the KVA value equal to (29.5)/(0.9), or 32.8. Next step is to find the third leg using Pythagorean formula. KVAR squared equals 32.8 squared minus 29.5 squared, so KVAR equals 14.3. You add 27.6 KVAR of capacitors, and you will get your .9 pf.

I got the same results...

 

Ingenieur

Senior Member
Location
Earth
have
29.5/51.2 = 0.58
41.9 kvar

want
29.5/newkva = 0.9
newkva = 32.8

from kva = sqrt(kw^2 + kvar^2)
32.8 = sqrt(29.5^2 + newkvar^2)
newkvar = sqrt(32.8^2 - 29.5^2) = 14.3 kvar

need to add 41.9 - 14.3 = 27.6 kvar
 
Last edited:
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
The algebra is not altogether complex. But beware of harmonics.

Even have some of that in there.

HzKVAscKVAR
H (HARMONIC FREQ)22.17491.351.00
15.67491.352.00
12.80491.353.00


That and I have an email this morning inviting me to read a white paper on "How PFC Capacitors Affect Harmonic Levels" @powerermonitors.com.

Study time again.

Have I ever mentioned I'm counting days to retirement and an EC business is available?
 

Besoeker

Senior Member
Location
UK
Even have some of that in there.

HzKVAscKVAR
H (HARMONIC FREQ)22.17491.351.00
15.67491.352.00
12.80491.353.00


That and I have an email this morning inviting me to read a white paper on "How PFC Capacitors Affect Harmonic Levels" @powerermonitors.com.

Study time again.

Have I ever mentioned I'm counting days to retirement and an EC business is available?
Sub harmonics. Those that are multiples of supply frequency are usually more troublesome for PFC. We are a 50Hz country and most put detuning reactors with a resonant frequency of 225Hz so a bit below 5th. I designed for 177Hz. A bit more expensive but it did the job.
 