Places to Apply 240.4(B)

Status
Not open for further replies.

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
For C-1, 230.90(A), exception No. 3. is more relevant than 240.4(B).

For the 60A feeders, 240.4(B) may not apply in a practical sense...#8 has an ampacity of 50 and #6 has an ampacity of 65, so using #6 you are already above the 60A OCPD.
If the ampacity of the 60A feeders was corrected for temperature, putting the ampacity below 60, then 240.4(B) could apply.
 

Gshell82

Member
Location
Boston
So now I am thinking I definitely cannot apply it to C-1, C-2 and C-4 since those cables are not protected by the Service Disconnects and 240.4(B) is based on the cable OCPD size.

Agreed?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
So now I am thinking I definitely cannot apply it to C-1, C-2 and C-4 since those cables are not protected by the Service Disconnects and 240.4(B) is based on the cable OCPD size.

Agreed?

I think 230.90(A) Ex No. 3 would apply to C-1 and 230.90(A) Ex No. 2 would apply to C-2 and C-4
 