Patient Care receptacles? 517.16

Status
Not open for further replies.

nietzj

Senior Member
Location
St. Paul, Minnesota
Occupation
Electrician
This is really throwing me off. 517.16 says isolated ground receptacles are not allowed in a patient care vicinity. If I want to install a hospital grade rec in the patient care area what else are my options?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I just looked and noticed most were hospital grade and isolated ground. Looks like I can just install hospital grade and be good.

What makes you think they are isolated ground and hospital grade, do they have a green dot and a triangle as well?

Roger
 