I am currently bidding a mixed use medical facility that also will house a dental office. Are there any special considerations that are unique to dental offices. Looking for useful advice from people who have experience in this specific application.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
HCF MC cable for the receptacle circuits along with hospital grade receptacles in the treatment rooms. That's what 517.13 says. Lighting, waiting room, offices and restrooms are regular occupancy.

-Hal
 

tw1156

Senior Member
Location
Texas
I am currently bidding a mixed use medical facility that also will house a dental office. Are there any special considerations that are unique to dental offices. Looking for useful advice from people who have experience in this specific application.

406.12(5) (NEC 2017 if applicable).

Tamper Resistant Receptacles in business offices, corridors, waiting rooms, and the like in clinics, medical and dental offices and outpatient facilities.
 