    I am aware that there are UL listed under cabinet strips available, and that there is a listing for them. I have a great connection on getting flexible LED strips from a supplier that I've used a lot. The strips are 12V, but not UL listed. I've looked under Art 410, and I'm just not 100% that I'm interpreting the text correctly. So the question is, are 12V LED strip lights required to be UL listed to be installed legally according to the NEC?
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,032
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You were in the wrong Article and yes you need listed LEDs
    ARTICLE 411
    Lighting Systems Operating at
    30 Volts or Less
    411.1 Scope. This article covers lighting systems operating
    at 30 volts or less and their associated components.
    411.3 Listing Required. Lighting systems operating at
    30 volts or less shall comply with 411.3(A) or 411.3(B).
  3. #3
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    As Iwire stated - listed yes, but it does not have to be UL there are other NRTLs.
    Listed. Equipment, materials, or services included in a list
    published by an organization that is acceptable to the authority
    having jurisdiction and concerned with evaluation
    of products or services, that maintains periodic inspection
    of production of listed equipment or materials or periodic
    evaluation of services, and whose listing states that either
    the equipment, material, or service meets appropriate designated
    standards or has been tested and found suitable for
    a specified purpose.
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #4
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,601
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    110.3(B) also, IMO, requires listing
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  5. #5
    Join Date
    Jan 2009
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    How so? All that says if it is listed, we gotta follow instructions. Lotsa stuff we use does not require listing.
    (B) Installation and Use. Listed or labeled equipment
    shall be installed and used in accordance with any instructions
    included in the listing or labeling.
    Derek
  6. #6
    Join Date
    May 2012
    United States
    Posts
    10
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Interesting point jumper. So would it be the AHJ that would determine which NRTL are accepted, or would it be NEC that determines that? And, if it is the NEC that determines which NRTLs are acceptable, where would I find such information? I know that these LEDs that I'm referring to do have some testing certs... just have to go find out which ones, and if they're acceptable.
  7. #7
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,201
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by billiards4me View Post
    OSHA recognizes NRTL's and has a list of NRTL's that they recognize.
    Chris
  8. #8
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,201
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I disagree that 110.3(B) requires listing. 110.3(B) states that listed and labeled equipment must be installed in accordance with any instructions included in the listing and labeling. There is nothing in 110.3(B) that requires anything to be listed.
    Chris
  9. #9
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,601
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by raider1 View Post
    Chris
    Well I knew someone would argue that however- it states "listed or labeled equipment shall be installed and used in accordance with"....
    I read it as listed equipment shall be installed and shall be used according...
  10. #10
    Join Date
    Jan 2009
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I see your point, but that would mean everything we install or use would have to be listed for that specific purpose. No?