    How can you pass cables through a fire-rated wall and keep "free air" ampacities?

    I have a set of cables in free air that I need to pass through an 8-inch cinder block fire-rated wall and then in free air back to the transformer. I would like to use the "free air" ampacity ratings from Table 310.15(B)(17). Is there anyway to pass through a free-rated wall and keep the "free air" ampacity ratings?

    1. One approach is to transfer the cables to a cable tray, in a single layer with over a diameter space between per 392.80(A)(2)(c). Then use a cable tray wall penetration sleeve with fire stop blocks. However, the cables will no longer be in free air for the 8 inches it is encapsulated by the fire stop material. So I can increase the size of conductors to get a necessary ampacity. Are there any exceptions for small lengths of "free air" cables not being in free air for small lengths (such as 8" out of a 50 ft run)?

    2. Another option is to mount a fire-proof splice box of some sort at the wall. Attach cables to terminals on either side of the wall. Are there products that are designed for passing through fire-rated walls? Possibly use a wall penetration bus duct with cable terminals on each side.

    I am curious if anyone has any creative ideas.

  2. #2
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    3,585
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    See 310.15(A)(2) exception.

  3. #3
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Conductors sleeved in a raceway 24" or less need not be derated.

    310.15(B)(3)(a)?

    (2) Adjustment factors shall not apply to conductors
    in raceways having a length not exceeding
    600 mm (24 in.).
    "Electricity is really just organized lightning." George Carlin