mccayry

Senior Member
Location
Tennessee
Im looking for about a 3 circuit panel for a swimming pool. I will be feeding the pump (8.8Amps) and a receptacle(15Amps). I would like to find a panel that comes with a 15A or 20A DP GFCI breaker. I found one online but it comes with a 50A DP GFCI, I guess for a spa or hottub. This will be my first pool so I thought some of you guys that do alot of these would know of a good setup. Thanks in advance for the info.
 

Cavie

Senior Member
Location
SW Florida
Im looking for about a 3 circuit panel for a swimming pool. I will be feeding the pump (8.8Amps) and a receptacle(15Amps). I would like to find a panel that comes with a 15A or 20A DP GFCI breaker. I found one online but it comes with a 50A DP GFCI, I guess for a spa or hottub. This will be my first pool so I thought some of you guys that do alot of these would know of a good setup. Thanks in advance for the info.

Seamins has a 4 ckt. They don't come with breakers. You buy what youn want
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
with an inground you will be extremely lucky to get by with 3 circuits.
most of the ones I see have two pumps, often a light, receptacles, etc.
3 might be workable, but you might as well go larger. Negligible cost increase.
If this is your first pool, the panel will probably be the least of your problems :grin:.
680.24, 680.26 are usually the "killers"
 

mccayry

Senior Member
Location
Tennessee
I was asked to give an estimate for this job and yes this is my first pool. The HO has said that the pool man is using 1 pump which draws 8.8A @240V. My thinking was to run a 30A circuit from main panel to the panel @ the pool. The pump will be on a 15A DP GFCI breaker controlled by a timer and of course a 15A GFCI receptacle for 680.22(A)(3). How does that sound?
 

cpinetree

Senior Member
Location
SW Florida
another thought

another thought

You might run 12/4 MC and not use a sub panel at all. Just be sure to keep the ground continuous if you have a light transformer.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You might run 12/4 MC and not use a sub panel at all. Just be sure to keep the ground continuous if you have a light transformer.

This could work if the pool panel is on the same structure as the main panel. A 30 amp circuit would work as described above.
 