    I'm new to the forum, but am a Journeyman Electrician in Austin, TX. I'm starting to learn about transformers and I've searched the hell out of this site for an explanation that I understand but to no avail...
    My Question:
    How does a Delta High Leg get 240V from leg to leg, but get 208V from the High Leg to Ground, when the other Legs get 120V to Ground?
    I know there's a calculation - 120V x 1.73 = 208...but that equation doesn't explain the HOW I guess. Every diagram I see of Delta transformers make visual sense to me...but how does it happen? If there's 240V from A to B, and B to C...shouldn't all 3 legs have the same voltage to ground?
    I still don't really know why Wye transformers have a ground and Delta's do not so maybe that's where my lack of understanding lies.
    Thanks for any info you have!
  2. #2
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,348
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    How good are you with the Pythagorean formula?
    Hypotenuse of triangle = 240V L-L
    Short leg of triangle = 120V L-N
    Missing Leg = ??V High L-N
    Just because you can, doesn't mean you should.
  3. #3
    Join Date
    Dec 2010
    Posts
    1,508
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Jim nailed it. Here is a picture for more help.
    Name:  Open delta.jpg
  4. #4
    Join Date
    Jun 2012
    Austin, TX, USA
    Posts
    121
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Wow. Thank you. I love this place lol...
    E=mc2 ...that is all.
  5. #5
    Join Date
    May 2008
    London, England
    Posts
    765
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    And BTW, some delta transformer secondaries are grounded, look up "corner grounded delta"
    The advantage of such a system is that three phase power is available for motors, but because one wire is grounded, only 2 pole circuit breakers and switches are needed, rather than 3 pole.
  6. #6
    Join Date
    Aug 2010
    Posts
    4
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Excellent post I must say.. Simple but yet entertaining and engaging.. Keep up the awesome work!
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,644
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by broadgage View Post
    The "delta high leg" system is grounded also otherwise there would be no "high leg" it is just grounded at a different point in the system.
  8. #8
    Join Date
    Jun 2012
    Austin, TX, USA
    Posts
    121
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Is it always the "high" leg that gets corner grounded?
    Thanks for the info
  9. #9
    Join Date
    Jun 2012
    Austin, TX, USA
    Posts
    121
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sabatini View Post
    I agree...I didn't think about the fact that each leg is 60 degrees apart so simple algebra once again solves everything lol. Why did I hate my Algebra teacher again?
  10. #10
    Join Date
    Dec 2010
    Posts
    1,508
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by teufelhounden91 View Post
    Thanks for the info
    No. You won't have a high leg on a corner grounded delta.
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts