Help me find this code reference

Status
Not open for further replies.

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
I have seen some language in the NEC... somewhere... that directs us to bond the grounded (not the grounding) conductor to an enclosure in some situation(s), but now I cannot find it. Anyone know where it is?

Help, not Heko; ko is next to lp. :D
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I have seen some language in the NEC... somewhere... that directs us to bond the grounded (not the grounding) conductor to an enclosure in some situation(s), but now I cannot find it. Anyone know where it is?

Help, not Heko; ko is next to lp. :D

Are you maybe thinking of 250.92?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
250.24(B) addresses bonding service enclosures to the grounded conductor and 250.142 lists the uses where a grounded conductor can be used for equipment grounding.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
Are you maybe thinking of 250.92?

No. The section I am recalling specifically requires the grounded conductor (usually the neutral) to be bonded to an enclosure. I believe it came up in one of the protracted discussions about whether a supply side connected PV system should be considered a separate service connection.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
250.24(B) addresses bonding service enclosures to the grounded conductor and 250.142 lists the uses where a grounded conductor can be used for equipment grounding.

That's sort of it but not exactly. Perhaps the reason I cannot find it in my 2014 codebook is that I am remembering it from 2011 and it got changed.

But thanks; 250.142 shows that what an AHJ is requiring of us (grounding a tap box on the line side of a service by bonding it to the neutral) is permitted.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You might take a look at 250.80 although I'd have used 250.92 as ggunn suggested
 