I have a inspector telling me I haft to bond my emt chases. These chases are going thru a fire wall for data wires. Is this a code I don’t know about?


News to me. "May become Energized, is the applicable wording I think of. So he would have to explain how they could become energized.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Short sections of raceway used as sleeves are not required to be bonded. Ask for a code reference.
 