I dinged (110.26(A)(1)) a facility a few months ago on this. There is a disconnect mounted on a wall and a metal platform located directly in front of it bolted to the floor.
Question: Could they raise this box up 6 1/2' off the platform and be in compliance? This would put the disconnect approx. 9' or so off room floor.
This is a chemical storage room and they use this platform to add chemicals to a tank located out of the picture.
They can't move it to the other side of the tanks because of existing utilities. Only options are to move the box further up on the wall or remove the platform (which they do not want to do).
Question: Could they raise this box up 6 1/2' off the platform and be in compliance? This would put the disconnect approx. 9' or so off room floor.
This is a chemical storage room and they use this platform to add chemicals to a tank located out of the picture.
They can't move it to the other side of the tanks because of existing utilities. Only options are to move the box further up on the wall or remove the platform (which they do not want to do).