    Conduit from above suspended ceiling into panel board without derating

    This might be an obvious question, and I'm just not creative enough to find a solution!

    I need to run about 40 branch circuits (all run with type MC cable) from above a suspended ceiling into a surface mounted panel board. The ceiling is at 12 feet and the top of the panel is at 6 feet, so I have a 6 foot gap to span.

    I would love to run just one 2" conduit from a box above the ceiling down into the panel, but since it would be over 24" long I would need to apply a derating factor according to 310.15(B)(3)(a). My next idea was to install a two foot metal trough between two sections of conduit so I could keep them under 24", but as I understand a trough would be considered a "metal wireway" so I would need to apply a derating fator if I had more than 30 current carrying conductors running through it (which I would) (376.22(B)).

    I would really like to avoid running 40 three-quarter inch conduits down into the panel (and its a finished room so running the MC straight down isn't an option)...what is the typical solution in a situation like this? I would imagine it would be a common issue (though this is the first time I am dealing with it so may be not...)

    Thanks in advance for your help!

  2. #2
    Join Date
    Jul 2007
    Posts
    3,103
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You would only have to derate the wire from the j box down to the panel, you just upsize the wire the proper amount.

  3. #3
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,527
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Can you run the mc down to the panel then box them in? Build a sheetrock box the same width and depth as the panel all the way up to the cieling.

  4. #4
    Join Date
    Feb 2003
    Location
    Huntsville Alabama
    Posts
    2,253
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Why not drop the MC's into the panel and have a sheet metal shop fab a skirt to cover them?
    Some people are like slinkies. They serve absolutely no useful purpose. But still put a smile on your face when pushed down a flight of stairs.

  5. #5
    Join Date
    Oct 2008
    Location
    Pennsylvania
    Posts
    17
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hillbilly1 View Post
    You would only have to derate the wire from the j box down to the panel, you just upsize the wire the proper amount.
    Correct me if I'm wrong, but since I would have over 41 current carrying conductors in the same conduit I would need to use a derating factor of 35. I started out with 12awg, so after derating I would need to use something like 4 awg!

    Quote Originally Posted by Buck Parrish View Post
    Can you run the mc down to the panel then box them in? Build a sheetrock box the same width and depth as the panel all the way up to the cieling.
    Quote Originally Posted by masterinbama View Post
    Why not drop the MC's into the panel and have a sheet metal shop fab a skirt to cover them?
    These are ideas that would certainly make it easier for me, I'll have to talk to the GC and see what he thinks about something like that. Thanks!

  6. #6
    Join Date
    Sep 2004
    Posts
    1,497
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You don't need a conduit per circuit, you can usually use 9 CCCs into a raceway withotu derating below "normal" if using 90C wire. So 5 conduits should do it, perhaps less if some of these are multiwire branch circuits
    Mark
    Kent, WA

  7. #7
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,298
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by masterinbama View Post
    Why not drop the MC's into the panel and have a sheet metal shop fab a skirt to cover them?
    Quote Originally Posted by Buck Parrish View Post
    Can you run the mc down to the panel then box them in? Build a sheetrock box the same width and depth as the panel all the way up to the cieling.
    I agree with these two.

    or install (5) 3/4" flex conduit with (8) MWBC.
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  8. #8
    Join Date
    Jul 2007
    Posts
    3,103
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by DPMin View Post
    Correct me if I'm wrong, but since I would have over 41 current carrying conductors in the same conduit I would need to use a derating factor of 35. I started out with 12awg, so after derating I would need to use something like 4 awg!





    These are ideas that would certainly make it easier for me, I'll have to talk to the GC and see what he thinks about something like that. Thanks!
    Drop two 2" conduits. Your box would have to be fairly big anyway because of the number of cables coming into it, along with all of the splices.

  9. #9
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    24,137
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Take a look at 310.15(A)(2) Exception. If your cable runs are longer than 60', you would not have to derate for the 6' conduit run.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)