120/208 3 phase ATS fitted to 120/240 3 phase genset

Status
Not open for further replies.

Goldy63

New member
Location
Salem
Hi all
I'm in the process at looking for an ATS to mate up to my 100KW 120/240 3 phase genset for my new building and found a real good deal on a 300 amp ATS. However, it is rated at 120/208. I've not yet tapped into utilities and am assuming it will be transformed to a three phase four wire delta. If so, could this ATS work?
 

kwired

Electron manager
Location
NE Nebraska
First you mentioned new building so you must confirm some things.

Is utility supply 120/240 three phase or 208/120 three phase? Answer to this may end up meaning your generator isn't really all that compatible with your needs as it would put a 208 volts to ground voltage on one of the phases when connected to generator when that phase only runs 120 volts when on the utility.

If you have 120/240 three phase from utility then you match with generator voltage and this just becomes a question if the 208/120 ATS is usable on this system. In that case it may or may not work depending on how it is designed.
 