Ampacity of Direct Burial Conductors

Status
Not open for further replies.

jason sleeth

Member
Location
Illinois
I have an installation in which the customer upgraded the size of his generator. I have installed a triplex "stephens" ALUM 2 awg, 7 strand, .403 inches. I have it buried under 36" in direct earth. The ampacity from the manufacturer states that it is good for 165 amp based on the NEC 2005. I need 145 amps. The length of the cable is 175'.

Can someone walk me through the NEC Calculation to determine the ampacity of the wire? I am unclear going through 310 on how to properly calculate the ampacity.

Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There's a basic clash between "Stephens" and the NEC as "Stephens" is a UD cable and not a recognized NEC conductor, is not listed in Art 310, and normally is not acceptable on NEC covered installation.
Under NEC installs a #2 AL would normally be a 90 amp conductor.
 

iwire

Moderator
Staff member
Location
Massachusetts
For what it is worth, 145 amps, 175' 2AWG AL results in more than 7.2% voltage drop.

Unless this is the 'main feeder' to a dwelling unit 2 AWG AL is limited to 90 amps and you can't even roll it up to 100.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Can someone walk me through the NEC Calculation to determine the ampacity of the wire?
This is not a "walk through" situation. Calculation of ampacity for underground installations is a highly complex mathematical problem that involves dozens of variables. The bad news is that you need a computer program (those are not cheap) and a licensed professional engineer (we are not cheap either) to perform such a calculation. The really bad news is that the results are almost always lower than the values shown in table 310.16. So if you are hoping to get a little extra maneuvering room by using a calculated value, rather than a tabulated value, it is time to give up that hope. Sorry.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
This is not a "walk through" situation. ,,,,,,,,,,,,,,,,,,,,,,,,,,,,,, and a licensed professional engineer (we are not cheap either) to perform such a calculation. ,,,,,,,,,,,,,,,,,,,,,,,,,,,,.

but , normally, worth every nickle.
 

jason sleeth

Member
Location
Illinois
The spec sheet states that it is UD but is rated for multiple insulations.

The spec sheet indicates the wire is ICEA s-105-692UL standard 854 for type USE-2 Federal Specification JC-30BNEC.

It also states that ampacity 90 degrees C, Conductor temperature 20 degree's celcius ambient, RHO50, 100% Load factor.

I am guessing the correct formula used for the engineer is 310.15 (C)

The RHO might be the value of thermal resistivity

I need to look through annex B then I will get back to you.

The amacity of conductors in free air greatly increases the amacity you are allowed on a conductor.

Direct Burial allows the heat to disapate in the ground plus the abient temp is about 57 degrees F

I do not think you are limited to the 90 amps in this scenario but that is why I am asking the more experienced electricians out there
 

jason sleeth

Member
Location
Illinois
For what it is worth, 145 amps, 175' 2AWG AL results in more than 7.2% voltage drop.

Unless this is the 'main feeder' to a dwelling unit 2 AWG AL is limited to 90 amps and you can't even roll it up to 100.

You are right. There would be an issue with Voltage Drop. Thanks.
 