can you pigtail a 20 amp circuit with #14 wire as long as the tail originates in the box and does not leave the box?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
can you pigtail a 20 amp circuit with #14 wire as long as the tail originates in the box and does not leave the box?

I am leaning toward the opinions of the other guys here, but I have a question for the op and the others. What does the pigtail feed?

Wouldn't 210.19(4)(exceptions) come into play? Not for a receptacle I know...
 
there are few exceptions, but i doubt they apply to your situation, but we really dont know what it is. 240.4 D3 spells it out very plainly that 14 awg mustn't exceed 15 amp overcurrent protection.
 

jusme123

Senior Member
Location
NY
Occupation
JW
I think 210.24 allows for #14 taps up to 40 amps.:happyyes:

for receptacles :happysad:, #14 AWG for receptacles has to be protected by 15 amp ocpd maximum, whether tapped or connected directly to the receptacle
 