    Shared Neutrals

    What section in the code will give me direction on shared neutrals? I'm doing some work in an older building and they have as many as 11 20A/1P breakers on a single neutral conductor, on a 3PH panel. They are trying to aviod rewiring the entire building, but some of this work clearly needs to be redone.

    Is there a section I can reference when stating my case.

  2. #2
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,758
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    For code cycles before 2011, article section 225.7 was the closest you will find, it specifically allowed it for outside lighting but, with this being the case and nothing else where prohibitting it it seemed it could be used for other applications as well.

    Roger
    Moderator

  3. #3
    Join Date
    Oct 2012
    Location
    Princeton, NJ
    Posts
    30
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I stumbled upon 215.4, I think I found what I'm looking for.

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,883
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rjken1969 View Post
    I stumbled upon 215.4, I think I found what I'm looking for.
    So is this a feeder or a branch circuit. Certainly you can feed a panel with one neutral however there are limits to branch circuits.

    For the 2011 look at 200.4 but these installs were done before then as Roger was mentioning.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #5
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by roger View Post
    For code cycles before 2011, article section 225.7 was the closest you will find, it specifically allowed it for outside lighting but, with this being the case and nothing else where prohibitting it it seemed it could be used for other applications as well.

    Roger
    I agree. Nothing specifically prohibited a common neutral for MWBC's prior to 2011 NEC.
    I will have achieved my life's goal if I die with a smile on my face.

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,666
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rjken1969 View Post
    I stumbled upon 215.4, I think I found what I'm looking for.
    Keep in mind 215 is for feeders not branch circuits.

  7. #7
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,539
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rjken1969 View Post
    What section in the code will give me direction on shared neutrals? I'm doing some work in an older building and they have as many as 11 20A/1P breakers on a single neutral conductor, on a 3PH panel.
    Can you explain how this didn't burn up over time? Was the single neutral oversized?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,666
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Can you explain how this didn't burn up over time? Was the single neutral oversized?
    Depending on the loads:

    Loads were lucky enough to be reasonably balanced and no significant overheating occurred?

    Circuits were lightly loaded, or maybe little demand most of the time.

    If there would have been 12 circuits instead of 11 and all were identical load, the neutral current should be zero. Assuming they are all in demand simultaneously - which could possibly happen if this is lighting circuits.

  9. #9
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    20,353
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Depending on the loads:

    Loads were lucky enough to be reasonably balanced and no significant overheating occurred?

    Circuits were lightly loaded, or maybe little demand most of the time.

    If there would have been 12 circuits instead of 11 and all were identical load, the neutral current should be zero. Assuming they are all in demand simultaneously - which could possibly happen if this is lighting circuits.
    Until somebody turns on exactly the right (wrong) combination of 6 of the 12 lighting circuits.

  10. #10
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,539
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I guess that would depend on what type of lighting loads. Do you think that if they all were fluorescent lighting loads the neutral would have burnt up a long time due to triplen harmonics?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted