does the opening for a LV camera conduit that penetrates building Vinyl soffit need to be sleeved and fire-caulked? Can it just be sealed with regular weatherproof caulk?
 

Attachments

  • 2012-01-26_09-25-08_587.jpg
    2012-01-26_09-25-08_587.jpg
    75.3 KB · Views: 0

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Well, fire caulk certainly isn't needed.

Roger
 

mstrmp3

Member
so there is nothing in the code book that stipulates it has to be fire-rated sealant? (I couldn't find anything)
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
so there is nothing in the code book that stipulates it has to be fire-rated sealant? (I couldn't find anything)

The need for fire caulk will be spelled out in the building code, not the electrical code. The closest you get is 300.21 which talks about fire stopping, but it's up to you and/or the engineer to devise the "fire-rated assembly". If you look at 3M's site, you'll find all sorts of UL pre-approved fire-rated assemblies using their products.

Since the soffit is very unlikely to be a fire-rated partition, I'm going to say you're home free. but as others have said, I'd weather caulk it.
 