Maximum nunber of wires in split bolt

Status
Not open for further replies.

Dbronx

Senior Member
Location
Colorado
I have a package unit and need tom install 2 heater coils no terminal block in unit. I want to use split bolts, there will be 5 wires in each split bolt ranging 10awg-6awg.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You will need to find a different splicing method.

110-14a.gif
 

kwired

Electron manager
Location
NE Nebraska
I have a package unit and need tom install 2 heater coils no terminal block in unit. I want to use split bolts, there will be 5 wires in each split bolt ranging 10awg-6awg.
Are these heater units all permitted to be connected to one circuit? May be good reason why they are not already run to a terminal block.
 