User Tag List
Results 1 to 4 of 4
Thread: Sealing conduit with silicon
  1. #1
    Join Date
    Dec 2008
    Posts
    252
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I have conduits that run from interior boxes out to exterior light fixtures. The exterior boxes are filling with water from condensation. Should I seal the seal tight conduit with silicon caulk or is special electrical caulking required?
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,032
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If it is condensation duct seal should do it.
    Besides the NEC requires sealing conduits in some applications.
    300.7 Raceways Exposed to Different Temperatures.
    (A) Sealing.
    Where portions of a raceway or sleeve are
    known to be subjected to different temperatures, and where
    condensation is known to be a problem, as in cold storage
    areas of buildings or where passing from the interior to the
    exterior of a building, the raceway or sleeve shall be filled
    with an approved material to prevent the circulation of
    warm air to a colder section of the raceway or sleeve. An
    explosionproof seal shall not be required for this purpose.
  3. #3
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,452
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mlnk View Post
    You might want to also consider some kind of drain.
    Bob
  4. #4
    Join Date
    May 2013
    Massachusetts
    Posts
    2,476
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    BTW, it is silicone caulk, not silicon caulk. Silicone is to silicon, as polyethylene is to carbon.