User Tag List
Results 1 to 3 of 3
Thread: Panelboard wire bending space
  1. #1
    Join Date
    Mar 2014
    Baton Rouge, LA
    Posts
    171
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I have a 600 amp I-Line panel board. It has a square d, 3 pole subfeed kit (that feeds another panel) installed in one of the branch breaker positions with parallel 350 MCM conductors landed on it. For wire bending space I believe I can use 312.6(A), 1 wire per terminal value of 5 inches as the subfeed kit has 3 lugs per pole. Is this correct or do I have to use the 8 inch value?
    Also the current conductors for the circuit exit the back of the panel, are there minimum distance requirements for how far these conduit entries must be from the terminals of the subfeed kit?
    Input, feedback, ridicule? All welcome. Thanks.
  2. #2
    Join Date
    Sep 2014
    dallas tx
    Posts
    1,640
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This may not apply but I'll offer it.
    We ran feeders for a MCC that was 900 amps or close too. The MCC had its own main breaker installed.
    The ahj said 13" was the minimum distance from entry to breaker for our situation. I think we had 11"
    I had to retap the mounting assembly for the breaker to be 13.5. "
    The hardest faults to clear are mine
  3. #3
    Join Date
    Mar 2014
    Baton Rouge, LA
    Posts
    171
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electricalist View Post
    thanks for the feed back.
Tags for this Thread
Posting Permissions
  • You may not post replies
  • You may not edit your posts